Re: Structural Load

2020-06-03 Thread Skyler Bilbo via Sprinklerforum
The structure needs to support a larger point load (with a very complex explanation, it probably does). Otherwise, if a guy working on the roof were to stand on one foot, the structure could potentially collapse. Structural engineering calculations are extremely complex (I would say more so than

RE: Structural Load

2020-06-03 Thread Steve Leyton via Sprinklerforum
Ron beat me to it – this is NOT your problem. I’m assuming it’s an existing structure or a lightweight metal frame if new? From a responsible charge perspective, I think you have to perform your due diligence and consider every reasonable option regarding type and spacing of hangers, then

Re: Structural Load

2020-06-03 Thread Ron Greenman via Sprinklerforum
And remember the building does not belong to you and it is NOT your responsibility to come up with a solution. The owner, via his representatives (the GC, the structural engineer, and ultimately, the architect) is responsible for building a code-compliant building that includes supporting any live

Re: Structural Load

2020-06-03 Thread John Denhardt via Sprinklerforum
I agree with Ken. I have been down this road before. The structure needs to support the piping plus 250 pounds at the point of hanging. If the structure can handle this load, then the structure has an issue. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical

Re: Structural Load

2020-06-03 Thread Parsley Consulting via Sprinklerforum
Jerry, Although I'm slightly unclear over what you're being told I would make sure that whoever is providing that information to you has read 9.2.1.3.1 of the '16 edition of -13: 9.2.1.3.1 Sprinkler piping shall be substantially supported from the building structure, *which must

Re: Structural Load

2020-06-03 Thread cw bamford via Sprinklerforum
Building loads may use a different safety factor from the 2019 NFPA 13 table A.18.5.9 4" sch 1011.78 lbs/ft if hangers are every 10' that's 117.8 lbs at each hanger. hangers every 15' 177lbs. Sprinkler design safety factor is 5 times + 250 lbs they MAY design a 5 times dead load

Structural Load

2020-06-03 Thread Jerry Van Kolken via Sprinklerforum
I have a building where they are telling me the structural point loading on the framing less than 250lbs. (140lbs) Advice? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730

Re: Water Supply Test

2020-06-03 Thread BRUCE VERHEI via Sprinklerforum
I’m a little cautious without seeing a sketch to make sure I’m seeing the situation correctly, but yes, I’ve used alternate connection locations for the gauge. i know my water department has made a pair of matching taps on matching dead ends so we could make a series of test prior to major

Re: Water Supply Test

2020-06-03 Thread Mike B Morey via Sprinklerforum
For what it's worth, NFPA 291 is not a standard, it's a "recommended practice", also in most jurisdictions it's not adopted as a law/rule/etc. Also the only "body" material in NFPA 13 (and 24) states the volume and pressure are to be determined from waterflow test data or other approved

Water Supply Test

2020-06-03 Thread Jamie Seidl via Sprinklerforum
Hello Forum, I have an odd situation that I haven't come across before. We requested a water test and received a water test from the fire department for a project that incorporated a private hydrant. The test was performed on the private hydrant but since there was only a single hydrant on the