Make sure there are no electrical conduits or similar leading down through the 
floor to another space that is at a lower elevation. Stuff happens despite what 
others may claim. It is not unlike, "there is nothing to burn”. I’ve seen an 
installation, not a diesel fire pump but an emergency power generator, where a 
failure in the day tank resulted in the above ground diesel tanks siphoning out 
fuel at the generator which then traveled via the electrical raceways down to 
the basement electrical room at the adjacent building. Include planning for how 
the owner would prefer to handle that spill. The facility people often have the 
better perspective. They also have a say in the contract process.

Allan Seidel
St. Louis, Mo

> On Nov 20, 2020, at 8:02 PM, Ron Greenman via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I'm in the Bruce V. camp on this one. If your customer is worried about
> spillage at any point in the system then why not curb the entire pump room
> and raise the batteries, the pump, and all the ancillary stiff that might
> be on the floor above the level of a full spill as you'd do with the
> threshold (or I guess in this case the oilhold)?
> 
> 
> Ron Greenman
> 
> rongreen...@gmail.com
> 
> 253.576.9700
> 
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
> 
> 
> On Fri, Nov 20, 2020 at 3:07 PM BRUCE VERHEI via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
> 
>> I’m mostly impressed you have an owner who cares.
>> 
>> Best.
>> 
>> Bruce Verhei
>> 
>>> On 11/20/2020 4:19 PM Kyle.Montgomery via Sprinklerforum <
>> sprinklerforum@lists.firesprinkler.org> wrote:
>>> 
>>> 
>>> Our standard for diesel fire pumps is to provide a double-wall fuel tank
>> with leak detection, steel supply and return fuel lines, and of course the
>> connection at the diesel engine is generally a flexible connection provided
>> with the diesel engine from the manufacturer.
>>> 
>>> Anybody doing anything different?
>>> 
>>> Any particular problems with leaks?
>>> 
>>> I've got a client who is particularly concerned about mitigating fuel
>> leaks, but in my experience there is little reason to be concerned about
>> leaks with this arrangement. The client is asking me to look at using the
>> special Kynar double wall pipe made by Flexworks. I guess the advantage is
>> that you would have less connections because it would bend rather than use
>> fittings (90s), but it looks like it would be more easily-damaged than
>> steel pipe. Anyone have experience with this or something similar?
>>> 
>>> We've also discussed possibly adding a curb below the fuel tank to catch
>> leaks, but what if the leak occurs in the line closer to the diesel engine
>> (outside of the curb)? The curb is useless at that point.
>>> 
>>> I feel like the standard method is pretty effective and that any of this
>> other stuff has seriously diminished return value, but I'd be interested to
>> hear from the audience.
>>> 
>>> -Kyle M
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to