Re: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-12 Thread Skyler Bilbo via Sprinklerforum
It sounds like the architect is working hard to inspire kids with his beautiful ceiling design... From the little information you gave, it may be more like a cloud ceiling than a traditional obstruction. See section 3.3.5.1 for the definition, and then 8.15.1.2.1.3 for criteria. You may also wan

Activity

2021-02-12 Thread Ron Greenman via Sprinklerforum
Seems like there's been a resurgence in activity in the list recently. Makes me happy and I know it would have made George Church happy. So in the spirit of George, or perhaps channeling George's spirit, if you are an active participant or a lurker that finds value in this exchange and you're a mem

RE: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
Does "at least 1 inch of space between each panel" mean several feet of space between each panel, or does it mean just a couple of inches. To me, it sounds more like you would have to treat them as grouped obstructions and protect underneath. -Kyle M -Original Message- From: Sprinkler

RE: Bathroom Chase

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
At first I thought this was Skyler and I couldn't figure out why he was disagreeing with me when I was agreeing with him. So then, Cecil, are you of the opinion that the entire area above the ceiling would need sprinklers? That doesn't make sense at all. We're essentially talking about a mecha

Noncontinuous obstructions More than 18" down

2021-02-12 Thread Dane Long via Sprinklerforum
Seeking others opinions I'm doing an Elementary school where in the commons area they have 4ft. by 8ft. tectum ceiling panels space throughout with at least 1" of space between each panel. These panels are slopes with the roof in one direct and then away from the roof in another. A8.6.5.3.3

Re: Multiple System Calculation

2021-02-12 Thread Ron Greenman via Sprinklerforum
This sounds like a job for more sheetrock. Oh, and more cowbell is always good. On Fri, Feb 12, 2021 at 10:57 AM Sean Conlin via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > See NFPA-13, 23.4.4.1.1.4 and 23.4.4.1.1.5. > > > > This should help you with the engineer. > > > Rega

Re: Bathroom Chase

2021-02-12 Thread Sprinkler Academy - C Bilbo via Sprinklerforum
While I think the logic path you follow for covering half a remote area one direction and then another makes some sense, the Committee was not willing to consider a two-sided scenario. The rule was written such that the area above the ceiling is only exposed on one side. This way, going two o

RE: Multiple System Calculation

2021-02-12 Thread Sean Conlin via Sprinklerforum
See NFPA-13, 23.4.4.1.1.4 and 23.4.4.1.1.5. This should help you with the engineer. Regards, Sean W. Conlin, A.Sc.T. Director Demand Sprinkler Design Inc. 37 Summerfield Crescent Brampton, ON L6X 4K4 T: 905-216-0922 C: 416-317-0028 E: scon...@demandsprinklerdesign.ca This message, including

Re: 13R Balcony Protection - Any Depth Requirements?

2021-02-12 Thread Mike B Morey via Sprinklerforum
FWIW this was born out of the fire code as a hedge against exposure fires from grilling, primarily, probably patio heaters and what not as well now. It then migrated into 13R due to the near universal pairing of IBC/IFC with 13R. IFC/IFC commentary unfortunately doesn't give a ton of wiggle e

Re: When is a Remote FDC required

2021-02-12 Thread J H via Sprinklerforum
A lot of times the civil engineer already has that figured out and if he shows it on the utility plan we go w/ his location and mirror the information on our site plan. Viru

13R Balcony Protection - Any Depth Requirements?

2021-02-12 Thread J H via Sprinklerforum
I notice that 13R 6.6.5.1 (2013 ed) requirement for sprinkler coverage for exterior balconies does not have a depth requirement unlike the 4ft rule found in 13. I have some apartments I'm bidding with a balcony at the upper level and the overhang is 3 ft.over the balcony. I'm going to put sprinkler

RE: Bathroom Chase

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
Brian, I agree with Skyler here. The picture may not look like what you're doing, but the book would be hard to carry if there were a figure representing every scenario. The intent seems to apply though: You've got a space that is sprinklered only because it is open to an adjacent sprinklered s

Re: Bathroom Chase

2021-02-12 Thread Nick Maneen via Sprinklerforum
IMHO, access for maintenance is not access for storage. Check out the door schedule. Maybe it is 2'-0" wide and locked for maintenance personnel only? On Fri, Feb 12, 2021 at 10:17 AM JD Gamble via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > But it has a door, most likely

Re: Bathroom Chase

2021-02-12 Thread JD Gamble via Sprinklerforum
But it has a door, most likely a “limited” access. I would say non sprinkled . just my 2cents Get Outlook for iOS From: Sprinklerforum on behalf of Brian Harris via Sprinklerforum Sent: Friday, February 12, 2021 7:53:58 AM To: sprinkl

RE: Bathroom Chase

2021-02-12 Thread Brian Harris via Sprinklerforum
JG- It is non-combustible but it is accessible. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of JD Gamble via Sprinklerforum Sent: Friday, February 12, 2021 9:31 AM To: sprinklerforum@lists.firesprinkler.org Cc: JD Gamble Subject

RE: Bathroom Chase

2021-02-12 Thread Brian Harris via Sprinklerforum
Skyler- Thank you. It doesn't look like the example shown in A.8.15.23.3 is the same situation I'm running in to. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Skyler Bilbo via Sprinklerforum Sent: Friday, February 12, 2021 9:2

RE: Bathroom Chase

2021-02-12 Thread tstone52--- via Sprinklerforum
Brian, Is this a Noncombustible Vertical Shaft? NFPA 8.15.2? And it sounds like it opens into a open concealed space above ceilings? Regards, G. Tim Stone   G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services      117 Old

RE: Bathroom Chase

2021-02-12 Thread JD Gamble via Sprinklerforum
Does the space meet the requirements of "Noncombustible and limited-combustible concealed spaces with limited access"? if so, should it be sprinkled? -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Skyler Bilbo via Sprinkl

Re: Bathroom Chase

2021-02-12 Thread Skyler Bilbo via Sprinklerforum
There is a section that talks about only going back 1.2 times the square root of the remote area beyond the ceiling. NFPA 13, 2013 edition, Section 8.15.23. Skyler Bilbo On Fri, Feb 12, 2021 at 7:25 AM Brian Harris via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > There's a

Bathroom Chase

2021-02-12 Thread Brian Harris via Sprinklerforum
There's a chase between (2) bathrooms that has an access door which I assume is for maintenance. The drywall stops 6" above ceiling, basically making the entire structure above the ceiling "open". I can't imagine we would need to provide protection at the deck throughout the whole area. Seems li