[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Very good point.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D9EFB2.8A0830B0]

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Micah Davis
What a great discussion this has been! I see it as my job to present a design to my customer, the AHJ, and the specifying engineer (and potentially other stakeholders) a design that attempts to address their respective concerns as we attempt to work together to provide a system that offers a

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
Let’s look at it another way: I have a two-riser standpipe system with 750 gpm demand; my water supply duration is 30 minutes, so I need to store 22,500 gallons. If I have a break tank that’s got water in it up to a point that floods pump suction (let’s say the water column is 6” over the

[Sprinklerforum] Re: ESFR Spacing

2023-09-25 Thread Brett Peters
I don't believe it states whether the spacing is along branches or between Max spacing is 12'-0 but max coverage is still only 100sqft Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. br...@proudline.ca 780 490 7602 office ext 202 780 490 7605

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Steve, I understand your point but the IBC says Secondary water supply. Thus a second water supply as a backup to the main or primary supply. 403.3.3 describes : An additional fire pump shall not be required for the secondary water supply unless needed to provide the minimum design intake

[Sprinklerforum] ESFR Spacing

2023-09-25 Thread Joe Burtell [MT-BILL]
Is the spacing of 12' in building less than 30' in table 14.2.8.2.1 of the 2019 NFPA 13 along the branchline or can it be between the branchlines? I feel it's along the branchline but can't find my confirmation. Joe Burtell | SET, CFPS Fire Sprinkler Manager D C 406-204-4653 406-861-4507 3004

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
We have designed and overseen construction of numerous PIP concrete tanks built into the parkade basements of high-rise buildings. We generally line them with a product that’s mostly polyurethane in composition, formulated to bond especially well with concrete.Inspection doesn’t require a

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
I think you’re blurring 403.3.2 and 403.3.3. If you need two separate city connections based on building height, you can still fill a break tank with supply lines connected to separate main legs as prescribed. 403.3.3 doesn’t say anything about the connection configuration of pump to tank

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Per NFPA 25 Tank internal inspection is required every five years. From: Travis Mack Sent: Monday, September 25, 2023 12:22 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Standpipe PRV Question That makes total sense and I can see where

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Travis Mack
That makes total sense and I can see where some projects I did in your area in the past were specified that way. I thought it odd, but I see the reasoning behind it now. Travis Mack, SET M.E.P.CAD | Instructor / Support 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
True, if your tank is down for maintenance… That occurs pretty infrequently, I’m sure we all agree. Like maybe once every 20 years or so? We take sprinkler systems in and out of service without any special consideration all the time and keep in mind that there are options for fire watch,

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Brett Peters
Steve, I understand the argument but I think that eliminates having two supplies to the fire pump, if you are only filling the tank and using the tank as the sole supply to the fire pump then you only have on supply, what happens if in the case of some type of event you actually lose the tank but

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Travis Mack
Steve: I was envisioning that you had your city supply going to the tank and you had the full tank. So if there is activation, you have either city supply or tank as back up. That is no issue. But if there is no direct bypass around the tank, then when your tank is down for maintenance,

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
Respectfully don’t concur. The point of the tank is to store a reserve of standpipe water or sprinkler water, whichever volume is highest given demand x duration. This requirement is intended to mitigate interruption of the primary water supply (city main) due to a cataclysmic seismic event

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Eric Rieve
Micah, To add to what Anthony just posted, I think the key point that may have been missed in your initial question is that the secondary water supply needs to be “automatic” all on its own. This means that is needs to be equivalent to the city water supply in available gpm and pressure before

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Jackie Ward
We utilized a secondary pump with tank supply, as Mr. Carrizuosa explains below, on a project recently. Our challenge was the tank had to be located underground because there was not enough room in the basement and we had to be very carefull with our vortex plate elevation to avoid exceeding

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Travis Mack
In my opinion, that is not dual water supplies. If the tank is down your water supply is down. You need one connected to the city and one connected to the tank. Yes. It can be quite tough to balance that calc. I’ve had to put a PRV on the incoming line so as to basically kill most of the supply

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Micah, We typically design ours with a primary pump taking suction from the city main and a secondary pump taking suction from the tank. The primary is of course designed to provide the required pressure to meet the standpipe design. The secondary pump is sized to provide an equivalent pressure

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Micah Davis
Thank you for the response, Steve! Does the redundant fill valves for the tank satisfy the secondary supply requirement of the IBC without an additional tank? I was interpreting the city main connected to the pump as the primary supply and the tank as the secondary supply (or vice versa). If my

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Steve Leyton
Micah: The best way to stabilize the pump discharge pressure and give yourself a (nearly) straight line suction pressure curve is to arrange the required secondary water supply as a break tank. Fill the tank with city water (recommend to manifold at least one automatic plus one manual fill;

[Sprinklerforum] Standpipe PRV Question

2023-09-25 Thread Micah Davis
Good morning, Forum! I've got a head-scratcher and am interested in the Forum's collective opinion! Important project parameters are as follows. - 42-story high rise with an automatic standpipe - Seismic Design Category - C - IBC 2018 - Fire pump supplied by city water supply - Secondary