[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Ken Wagoner
Tim is correct, and I caution those on this forum not to confuse "bracing" with "restraint" as -13 clearly identifies them as two different approaches.  From the '16, §9.3.6.1 identifies restraint as a lesser degree of resisting loads.  This is repeated in the '22 in §18.6.1. It's important

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Brett Peters
Also in section 9.2.3.7 Sprigs. Sprigs 4 ft (1.2 m) or longer shall be restrained against lateral movement. At one time it was only required in seismic areas but since 2013 it is required on any sprigs 4' or longer, as I understand it. Thanks Brett Peters General Manager Installation & Design

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Brett Peters
9.3.6.6 Sprigs 4 ft (1.2 m) or longer shall be restrained against lateral movement. Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. br...@proudline.ca 780 490 7602 office ext 202 780 490 7605 fax 780 777 0568 cell 780 718 2676 24h Visit us at

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread tstone52
2013 edition of NFPA 13, 9.3.6.6, Sprigs 4’-0 or longer shall be restrained…. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread matthew.willis1
It’s a general hanger requirement. Not in the seismic section.. R/ Matt Please rate our customer service Matthew J. Willis, CWBSP, CET Engineering Manager – Southwest Region FERGUSON FIRE DESIGN, LLC A Wholly Owned

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Jeff Werre
Where does the requirement to brace a sprig up at 4 feet come from? Thank you- Jeff Werre, CFM Plan Review and Inspection Specialist Development Services City of Goodyear, Arizona 1900 North Civic Square Goodyear, AZ 85395 c 602 316-0704 w goodyearaz.gov e

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread Bob Caputo
George, An arm over to a single sprinkler is defined as an arm over whereas when two sprinklers are served, it’s considered a branch line. Branch lines require restraint. If the arm over is to a sprig up longer that 4ft, the sprig requires restraint. I am not aware of a requirement to restrain

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread George Medina Jr.
I have an armover that is 2'-4" in length. The SEOR is requiring me to put a diagonal brace on the branch line that the armover is supplied from and a restraint on the armover ( I had left a branchline restraint detail from my template and I probably should not have left it on with these small

[Sprinklerforum] Re: 1" Armover Restraint

2023-10-19 Thread George Medina Jr.
I have an armover that is 2'-4" in length. The SEOR is requiring me to put a diagonal brace on the branch line that the armover is supplied from and a restraint on the armover ( I had left a branchline restraint detail from my template and I probably should not have left it on with these small