LOL guess I’m not quite as quick as Kevin just yet.
From: Steve Leyton
Sent: Friday, November 10, 2023 2:12 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Flow test adjustment formula
Yep.
From: Eric Rieve mailto:e...@rievefire.com>>
Sent:
Yep.
From: Eric Rieve
Sent: Friday, November 10, 2023 11:09 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Flow test adjustment formula
Steve,
It should be:
[cid:image001.png@01DA13C6.BE13EC40]
Where:
Px= The residual pressure at a partic
Steve,
It should be:
[cid:image001.png@01DA13DF.08481F30]
Where:
Px= The residual pressure at a particular flow (Qx)
Ps= The static pressure during the flow test
Pr= The residual pressure during the flow test correlating with Qr
Qx= The flow amount correlating with residual pressure being solved
Thanks Jamie.
I just got it from Kevin Hall – I should have called tech support in the first
place…
SL
From: Jamie Seidl
Sent: Friday, November 10, 2023 11:05 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Flow test adjustment formula
If
If I remember correctly, you can convert your outlet (Flow and pressure) to
a K factor K=Q/√P then just solve for P with your flow number (Q/K)₂.
Jamie Seidl
On Fri, Nov 10, 2023 at 1:28 PM Steve Leyton
wrote:
> Happy Friday everyone:
>
> Once I’ve taken a flow test, I know the formula for adj
Happy Friday everyone:
Once I’ve taken a flow test, I know the formula for adjusting the flow at a
particular residual pressure; it’s published in NFPA 291. But I’ve lost my
notes on the corollary formula for calculating the residual pressure at a
particular flow – does anyone have that hand