An emergency generator serving just the pump or a generator serving
other/additional building needs (such as a hospital/Life Safety Code)
satisfies the requirement for back up to the electric motor driven fire
pump.  

A back up isn't necessarily required by NFPA 20 unless your power source
isn't reliable or unless there are other considerations for the requirement.
Have I missed your point?


Bob Caputo, CFPS
657 Cantara Lane - Vista, CA 92081
Fire & Life Safety America Company
3017 Vernon Rd - Richmond, VA 23228             
Office: (804) 222-1381  Cell: (804) 263-1577
                           
                       




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 4:18 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Fire Pump Alternate Power

NFPA 20 (2007) Article 9.3.3 states "An alternate source of power is not
required where a back-up engine driven or back-up steam turbine driven fire
pump is installed in accordance with this standard."

Does the use of an emergency generator serving only the fire pump (no other
power) qualify as a back-up engine driven fire pump?



Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:    Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to