[Sprinklerforum] Re: Dry System Aux. Drain

2024-01-03 Thread dlm
Because of this issue I have added a requirement to my specs for the contractor to install a framed 11 X 17 diagram of the system with all of the valves shown and highlighted and mount it to the wall near the riser. David L. Miller, P.E. Engineered Fire Protection, LLC 11920 Richcroft

[Sprinklerforum] Re: Roof Drain / Sprinkler Drain

2023-08-23 Thread dlm
Re: “tying into the roof drain in the same stairwell” - Roof drains are not allowed within exit enclosures. Re: NFPA 101: 7.1.3.2.1(10) (2018 edition) - Penetrations into, and openings through, an exit enclosure assembly shall be limited to the following: (a) Door assemblies permitted

[Sprinklerforum] Re: System piping installed on top of a roof

2023-05-03 Thread dlm
I seriously doubt the building code will allow you to install anything on a roof without anchoring it down, no matter what the owner wants. You better not be in a hurricane or tornado prone area. Hurricane wind resistance is 140 mph in many cases. David L. Miller, P.E. Engineered Fire

[Sprinklerforum] Re: Combining dry system drains

2023-03-13 Thread dlm
Now that is interesting… The wording of the code is that tie-in drains are required, but the commentary says they should be avoided if possible. The 2022 edition (16.10.5.3.6) has the same wording in both the code and the commentary. David L. Miller, P.E. Engineered Fire

[Sprinklerforum] Re: Combining dry system drains

2023-03-13 Thread dlm
NFPA 13 (2016 edition) 8.16.2.5.3.6 Tie-in drains shall be provided for multiple adjacent trapped branch pipes and shall be only 1 in. (25 mm). Tie-in drain lines shall be pitched a minimum of 1⁄2 in. per 10 ft (4 mm/m). David L. Miller, P.E. Engineered Fire Protection, LLC 11920 Richcroft

[Sprinklerforum] Re: Spiral Blast Freezer

2023-02-22 Thread dlm
The only thing I can think of that might come close to applying would be 9.2.11 (2022 Edition) “Equipment Enclosures. Sprinkler shall not be required to be installed within electrical equipment, mechanical equipment, or air handling units not intended for occupancy.” However, I do not

[Sprinklerforum] Re: Rooftop Deck with Pergola

2022-06-28 Thread dlm
Excellent. That is exactly the interpretation I was hoping for. Thank you for the information. David L. Miller, P.E. Engineered Fire Protection, LLC 11920 Richcroft Avenue Baton Rouge, Louisiana 70814 225-273-5040 From: Jones, William - Fire Plans Examiner/Inspector Sent:

[Sprinklerforum] Rooftop Deck with Pergola

2022-06-27 Thread dlm
How does one handle a Rooftop Deck with a Pergola? The adopted version of NFPA 13 the 2016 edition. The pergola is, of course, combustible construction with joists 18" - 24" on-center, but there is no actual ceiling/roof. Technically, it is an "exterior projection off of the adjacent

"Uniform" Foam Coverage

2019-05-23 Thread dlm
As per usual, I am dealing with a rather unusual project. I am assisting, pretty much after-the-design, in obtaining approval of a system for protecting palletized plastic pellets in gigantic bags to a height of 14' under a roof with a slope of approximately 4:12. Of course, this slope exceeds