automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Warning! This email came from outside your company.
Travis-
Thanks. I should have mentioned I need it to be an upright. It's a retro-fit
job.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssyste
omatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
https://www.reliablesprinkler.com/files/bulletins/146.pdf?x76626
Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.
SPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD
From: Brian Harris
Sent: Monday, September 11, 2023 10:34 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Eric-
Thank you. I have an EOR that called for a K14.0 CMDA on a specif
11:48 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Brian,
To expand on this slightly, it's not that "general storage applications"
directly means class I-IV commodities, but that chapter 12 applies to
<http://bvssystemsinc.com/>
From: Ken Wagoner
Sent: Monday, September 11, 2023 11:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Brian,
Please remember that when you're looking for the required protection method for
storage, befor
tively to round out the rest of chapters.
[A close up of text]
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Brian Harris
Sent: Monday, September 11, 2023 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
E
Brian,
Please remember that when you're looking for the required protection
method for storage, before you begin selecting any protection method,
you must first identify these five things, at least.
* Commodity class
* Storage method (rack, shelf, etc)
* Packaging (cartoned, exposed)
* In
ing to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Brian,
Yes, it does per the "general storage applications" segment of the code section.
Eric Rieve, SET
Rieve Fire Protection
From: Brian Harris mailto:bhar...@bvssystemsinc.com>>
Sent: Monday, September
Brian,
Yes, it does per the "general storage applications" segment of the code section.
Eric Rieve, SET
Rieve Fire Protection
From: Brian Harris
Sent: Monday, September 11, 2023 11:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] CLASS I-IV / CMDA
Would 12.6.3 (NFPA-1