[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Larry Keeping
automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Warning! This email came from outside your company. Travis- Thanks. I should have mentioned I need it to be an upright. It's a retro-fit job. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssyste

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Brian Harris
omatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA https://www.reliablesprinkler.com/files/bulletins/146.pdf?x76626 Travis Mack, SET M.E.P.CAD | Instructor / Support 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com<http://www.mepcad.com/> | m: 480.

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Travis Mack
SPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD From: Brian Harris Sent: Monday, September 11, 2023 10:34 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Eric- Thank you. I have an EOR that called for a K14.0 CMDA on a specif

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Brian Harris
11:48 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Brian, To expand on this slightly, it's not that "general storage applications" directly means class I-IV commodities, but that chapter 12 applies to

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Brian Harris
<http://bvssystemsinc.com/> From: Ken Wagoner Sent: Monday, September 11, 2023 11:45 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Brian, Please remember that when you're looking for the required protection method for storage, befor

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Eric Rieve
tively to round out the rest of chapters. [A close up of text] Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Brian Harris Sent: Monday, September 11, 2023 11:32 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA E

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Ken Wagoner
Brian, Please remember that when you're looking for the required protection method for storage, before you begin selecting any protection method, you must first identify these five things, at least. * Commodity class * Storage method (rack, shelf, etc) * Packaging (cartoned, exposed) * In

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Brian Harris
ing to automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Brian, Yes, it does per the "general storage applications" segment of the code section. Eric Rieve, SET Rieve Fire Protection From: Brian Harris mailto:bhar...@bvssystemsinc.com>> Sent: Monday, September

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Eric Rieve
Brian, Yes, it does per the "general storage applications" segment of the code section. Eric Rieve, SET Rieve Fire Protection From: Brian Harris Sent: Monday, September 11, 2023 11:19 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] CLASS I-IV / CMDA Would 12.6.3 (NFPA-1