Scot,


A lot to unwrap in your diatribe but to the point, ICC is a code and most
NFPA documents are standards.  In simple terms, codes tells us when systems
are required and standards tell us how to comply in terms of design,
install, and maintenance.  Of course you know this.



I don’t want or need to post a dozen back and forth point by point debates
but my statement refers to the simple fact that NFPA standards are intended
to be interpreted by the local AHJ who has the authority determine what is
needed for their community.  NFPA standards are minimum requirements and it
is within the purview of an AHJ (by definition, an organization, office or
individual responsible for enforcing a code or standard, or for approving
equipment, materials, an installation or a procedure) to accept alternative
arrangements as noted in section 1.5 (Equivalency).



While I appreciate your perspective on the system of codes and standards,
every municipality is different and local AHJ’s have leeway to apply
requirements as they deem necessary.  Insurance companies are also an AHJ
by definition and their too is money and business decisions as opposed to
enforcing adopted codes or standards.



Let’s not twist or demean the system by invoking visions of mismanaged
pandemics.  I do not speak for NFPA but these consensus based codes and
standards have stood the test of time and keep people safe in the built
environment.  They are not perfect – few people are willing to pay for
perfection.  No code body or non-profit is going to provide legal support
for users of the documents, as they organization has zero control over how
they may be used or abused. NFPA’s committees are the most inclusive, open
and collaborative in terms of being consensus based on the planet.



Thanks for calling me out on my statement.







*Bob Caputo, CFPS*

*President*

*American Fire Sprinkler Association*

c:     760-908-7753

p:

214-349-5965 ext124

w:

firesprinkler.org

<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>



*Expand your business with ITM.*

Professionalize the role of your inspection team with AFSA’s comprehensive
20-month ITM Inspector Development program
<https://www.firesprinkler.org/itm> that provides a blended learning
environment teamed with robust curriculum created by top industry leaders.
Now enrolling for Spring 2022!



*From:* å... .... <eurekaig...@gmail.com>
*Sent:* Tuesday, March 15, 2022 2:51 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* [Sprinklerforum] Velocity - Rant leeway for the AHJ



NFPA standards provide wide leeway for the AHJ to make decisions, since
they are the ones who need to show up and fight a fire or access a building.



NFPA may provide wide leeway...on some subjects,

 but in reading of the administrative sections of NFPA and IBC,

  IBC to me clearly provides more--and more explicit permit for-- leeway.

And that is as it should be...

Why?

  Despite what some safety professionals might say, levels of  risk
tolerance or catastrophe acceptance -- VARY.

  Risk tolerance varies from locality to locality, from economic boom to
recession under inflation,

        from construction materials to labor skills... risk tolerance must
be flexible.



I see the IBC administrative chapter is written far more flexibly than the
NFPA administrative chapter.

In fact, NFPA seems to wash its hands entirely of any liability (see page 2
of every standard).

   While this disclaimer is transparent enough, it does not provide near as
much 'leeway' in supporting AHJs as IBC

IBC writes it will stand alongside and ?loyally? defend AHJ working in its
jurisdiction and with good faith,

     to the last court appearance.

I don't, and no one else should as well, expect IBC to be !loyal! to an
AHJ, just because that AHJ may say

   " hey, IBC building code trumps NFPA standards "

but we should *expect* IBC to provide legal support that is as open and
honest as possible.



several cans of worms have been opened here...

    a can of:   IBC vs NFPA vs most specific prescriptions vs contradictory
prescriptions

    a can of:   whoop yippie-kay-ya, regarding variability in risk tolerance



an example, si'll vous plait?

  May I have one can of COVID, please?

  Once upon a time, there was a thing called Hong Kong flu.

     It killed children too, not predominantly old, corpulent humans
already sick.

    There was a vaxx for this.  It was not mandatory.  No lockdown called
from uptown.

    I submit that the risk tolerance in 1968-69 was far, far greater than
it is in these mamsey-pamsey woken days.

  Risk tolerance changes,  not just over the last 50 years, but as one
crosses into states from red to blue ...

  Risk tolerance changes...so AHJ NEED engage this reality.

  It is the job of Mrs and Mr. Life Safety Engineer to document 'it':  this
level of risk tolerance  N.U.M.E.R.I.C.A.L.LY

  If a safety professional won't put a number on it with their signature,
they are acting above their pay grade.

    Document need simply be;  open, honest and simple.



  I give an interactive demo of this risk assessment documentation for any
AHJ program, anywhere...

  this offer is F.R.E.E for the safety community...

     although CEUs would be given to those who demonstrate functionality,
or

     at least the ability to cogently question this system's authority

     already, 5 SFPE chapters won't even respond to the offer,  guess they
are too busy

  NFPA does not endorse this, nor will they come out openly, honestly and
simply as to the real reason why...



The reason NFPA does not support this, is because SOMEONE

    sometimes openly, honestly and simply questions NFPA's authority.

    And IBC's.

   And my own.

  But I got little to no authority... only a soapbox, and loyalty to
efficiency, accuracy and transparency.

  Judgments that optimize accuracy, efficiency and transparency
threaten-to-the-core, those demanding loyalty.



' *The first duty of any citizen, is to question authority*"   -Ben Franklin

'* To criticize one's country is to do it a service...criticism, in short *

*       is more than a right, it is an act of patriotism-- a higher form of
patriotism ' *-Fulbright

'*Without deviation from the norm, progress is not possible*.'  - Zappa

'*I do not feel...that the same God endowing us with sense, reason &
intellect intended for us not to use them*'  -Galileo

*'All politics is local'*   - Tip O'Neil

*'Leeway or the highway'*   - Tip O'Deal



Scot Deal

Excelsior Fire & Risk Engineering

gms:  00 420 606 872 129









On Tue, Mar 15, 2022 at 10:16 AM Bob Caputo <bcap...@firesprinkler.org>
wrote:

Two separate issues:



There is no safety margin required by NFPA standards with regard to the
water supply test versus the system demand.  The annex recommends one but
the AHJ has the purview to require one.  I have tried many times, to define
a 10% or 5% required safety margin by submitting proposals to the NFPA 13
committee and none have passed.  Ken Isman from University of Maryland
(formerly from NFSA) also pushed this issue passionately but failed to
convince the committee that a safety margin is required, or that one can e
defined for every project.  If your project is in the already populated
area, you may not need one but if it’s a location where communities are
being developed or factories and warehouses are being planned, 10% might
not be enough.



The evaluation of water supplies is engineering as opposed to design.  A
registered professional engineer should evaluate all of the issues
surrounding a project to determine the adequacy of a water supply.  NFPA
standards provide wide leeway for the AHJ to make decisions, since they are
the ones who need to show up and fight a fire or access a building. It is
within the purview of the AHJ to add a safety margin to a water supply
where they determine one is needed.





The velocity issue is simple.  NFPA standards do not require or limit
velocities anywhere except for the suction side of a fire pump.  NFPA 13
and 24 did limit velocities many years ago but the reasons have long since
been dispelled.  People though at faster velocities, the Hazen Williams
formula was less accurate.  Joe Hankins once told me that FM’s velocity
limits were created because they didn’t want 1” grids or systems that
couldn’t be upgraded as tenants or owners changed hands or building uses.



The benefit of being old is knowing old stuff, as long as you can still
remember it







*Bob Caputo, CFPS*

*President*

*American Fire Sprinkler Association*

c:     760-908-7753

p:

214-349-5965 ext124

w:

firesprinkler.org

<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>



*Expand your business with ITM.*

Professionalize the role of your inspection team with AFSA’s comprehensive
20-month ITM Inspector Development program
<https://www.firesprinkler.org/itm> that provides a blended learning
environment teamed with robust curriculum created by top industry leaders.
Now enrolling for Spring 2022!



*From:* Byron Weisz <by...@cen-calfire.com>
*Sent:* Tuesday, March 15, 2022 9:18 AM
*To:* Michael de Gabriele <mpdegabri...@gmail.com>; Sprinkler Academy - C
Bilbo <prodesigngr...@msn.com>
*Cc:* travis.m...@mfpdesign.com; sprinklerforum@lists.firesprinkler.org
*Subject:* [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant



I think there are some good practices that need to be followed in the
design of fire sprinkler systems and sometimes “simpler” is better.
Treating the flow of water in fire sprinkler piping to other mechanical
systems are not comparable. The obvious is a fire sprinkler system is
designed for emergency use and other mechanical systems are in continuous
use. Sadly, most Mechanical Engineers who write specifications for fire
sprinkler design don’t understand the difference. I was taught that
velocity in fire sprinkler piping was irrelevant and to my knowledge there
is nothing stated in NFPA 13.



To continue the conversation there is no reference of a “safety margin” in
NFPA 13 either. I was told many years ago by this guy named Bob Caputo that
NFPA 13 allow you to design right to the design curve. Most jurisdictions
in the Republic of California give water flow data from either the Fire
Department or a Water Service Company to use for design of a system. This
information is usually doctored in some way. So why would a designer take
“doctored” water flow data and then include a 10% safety margin? Other than
to meet a local requirement there is no reason. What makes no sense at all
is to take “doctored” water flow information and use that information to
size a fire pump to design an ESFR fire sprinkler system.



Again, the best person to answer the questions of velocity and safety
margin in the design of a fire sprinkler system gracefully would be Bob.





*Byron Weisz*



*Cen-Cal Fire Systems, Inc.*

P.O. Box 1284

Lodi,  CA   95241

Phone (209) 334-9119

Fax      (209) 334-2923

Cell      (209) 993-8832

by...@cen-calfire.com



This and any attached documents are for the use of the intended
recipient(s) only and may contain information that is privileged,
confidential, or work product that may be exempt from disclosure under
applicable law. If you are not the intended recipient, any use,
dissemination, distribution, or copying of this communication and any
attachments is strictly prohibited, and you are hereby requested to delete
this message and any attached documents, to destroy any printed copies, and
to telephone or otherwise contact the sender immediately about the error.



*From:* Michael de Gabriele <mpdegabri...@gmail.com>
*Sent:* Tuesday, March 15, 2022 5:46 AM
*To:* Sprinkler Academy - C Bilbo <prodesigngr...@msn.com>
*Cc:* travis.m...@mfpdesign.com; sprinklerforum@lists.firesprinkler.org
*Subject:* [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant



You don't often get email from mpdegabri...@gmail.com. Learn why this is
important <http://aka.ms/LearnAboutSenderIdentification>

Hello All,

I hope that this email finds you well.

I practice fire protection in Australia, and recently the Australian
standards have removed the requirements for maximum pipe work velocity in
sprinkler systems.

We also design systems to NFPA and FM Global requirements when insurers
request upgrades, and as of late, the insurer on one particular project
queried the pipe work velocities. I couldnt find any reference to velocity
limitations in NFPA 13.

I still try and keep my sprinkler pipe velocities down to a reasonable &
practical value (6m/sec through valves and max. 10m/sec in pipe work as per
the older/superseded code).



I am curious though to whether the Hzen Williams Formula produces greater
errors as the Velocities Increase in the pipe? Has anyone ever seen a
limitation to the Formula or come across any articles to this effect?



Looking forward to your response / comments / advice



Kind Regards

Michael de Gabriele

Fire Protections Engineer

mpdegabri...@gmail.com



On Tue, Mar 15, 2022 at 10:48 PM Sprinkler Academy - C Bilbo <
prodesigngr...@msn.com> wrote:

Hi Travis,



I learned many years ago the reason velocity restrictions have persisted.
In systems that have running water, the higher velocities wear the inner
walls of the pipe/tube down over time.  The limits were intended to bolster
system lifetime.

Mechanical engineers are the largest group responsible for specifying
sprinkler systems and used the limits that seemed reasonable to them.

Of course, our systems are not flowing or circulating and these rules
should not apply to dedicated fire protection piping.  We have only
recently come away from having "closed loop circulating systems" being
defined in the NFPA 13 Standard.  And this is one of the reasons we used to
do that.

About the only requirement I have seen in Fire Protection was the old rules
from FM Global (last 10-15 years) where the underground systems had
limits.  I believe those have been gone for a while.

However, some MILSPEC and certain States still have some requirements
embedded in older sections of regulations.

Hope this helps.





It should be recognized that the above is my opinion as a member of the
NFPA, and has not been processed as a formal interpretation in accordance
with the NFPA Regulations Governing Committee Projects and should therefore
not be considered, nor relied upon, as the official position of the the
NFPA, nor any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Decatur, IL
217.607.0325
www.sprinkleracademy.com
ce...@sprinkleracademy.com
??
OUR STUDENTS SAVE LIVES!!
------------------------------

*From:* travis.m...@mfpdesign.com <travis.m...@mfpdesign.com>
*Sent:* Monday, March 14, 2022 5:41 PM
*Cc:* sprinklerforum@lists.firesprinkler.org <
sprinklerforum@lists.firesprinkler.org>
*Subject:* [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant



This was the “why” that I got:



We require a 10 psi margin for safety and to account for future degradation
of water supply.  The 14 fps insures that the piping will be larger and is
an added layer of margin for future development.



It wasn’t a fight the contractor wanted to go with since it was something
he missed in the specs.  They had no explanation as to why 14 fps.



Please rate our customer service
<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>



*Travis Mack, CFPS, CWBSP, RME-G, COC, SET*

*Senior Engineering Manager*

*MFP Design*

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com

www.mfpdesign.com



Send large files to us via: https://www.hightail.com/u/MFPDesign
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>



*From:* Ken Wagoner <k...@parsleyconsulting.com>
*Sent:* Monday, March 14, 2022 3:36 PM
*To:* Travis Mack <travis.m...@mfpdesign.com>
*Cc:* sprinklerforum@lists.firesprinkler.org
*Subject:* Re: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant



Travis,

I've run up against that a time or two myself.  It honestly baffles me how
those who have so limited an understanding of fire sprinkler systems
mandate what we do.

I've usually responded in one of several ways.

1st, I ask them to show me where in any applicable code or standard they've
found a limitation on velocities in above ground piping.  And, clearly, as
you and others have said - they can't because it isn't there.  As far as
NFPA is concerned it never was. A contact I had at NFPA a few years back
told me of an "engineer" who called him and wanted to know when that had
been removed from -13.  He did some research and found that it was never
removed, because it was never there in the first place. That didn't go over
well with the caller who was sure my contact was misleading him.

2nd, I acknowledge that the limitations on velocities in underground pipes
on public property are established as another poster observe to lessen the
deterioration caused from perpetually flowing water.  When I mention that
pipe sizing on public property is their purview, and what is installed on
private property they have no control over.  Usually my trump card in that
argument is to ask why backflow preventers are usually at or near the
property line.

3rd, and this works almost every time, I ask them to explain "why".  I
don't hear many responses to that which make any sense as far as fire
sprinklers go.

my thoughts only,

*Ken Wagoner, SET*


*Parsley Consulting500 West Mechanic StreetHarrisonville, Missouri
64701-2235*
*Phone: (760) 745-6181 *
*Visit the website*
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

On 3/14/2022 3:33 PM, travis.m...@mfpdesign.com wrote:

I totally realize where all this comes from.  It just amazes me at times,
how long incorrect information and lack of understanding of things can
remain in an industry.  I always challenge anyone to show me in a copy of
NFPA 13 anytime where it had velocity limits.  I’ve checked back as far as
the 30’s and could never find it.



People always say, I know it was in there at one time.



Please rate our customer service
<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>



*Travis Mack, CFPS, CWBSP, RME-G, COC, SET*

*Senior Engineering Manager*

*MFP Design*

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com

www.mfpdesign.com



Send large files to us via: https://www.hightail.com/u/MFPDesign
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>



*From:* Prahl, Craig/GVL <craig.pr...@jacobs.com> <craig.pr...@jacobs.com>
*Sent:* Monday, March 14, 2022 1:30 PM
*To:* Brett Peters <br...@proudline.ca> <br...@proudline.ca>; Travis Mack
<travis.m...@mfpdesign.com> <travis.m...@mfpdesign.com>
*Cc:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: [EXTERNAL] [Sprinklerforum] Re: Velocity - Rant



What Brett said.



I have had more “discussions” on velocity and pressure loss where the
challenger was quoting limits that are placed on totally unrelated type
systems. Try to explain to them that those rules do not apply to fire
protection systems and they’ll look at you like you’ve got a horn coming
out of your forehead.  I’ve also had these types of artificial limitations
placed by owners who have some “FP” person on staff who has never performed
a flow test or developed a hydraulic calculation but did stay at a Holiday
Inn Express which had sprinklers.



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |
craig.pr...@jacobs.com | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: email or MS TEAMS







*From:* Brett Peters <br...@proudline.ca>
*Sent:* Monday, March 14, 2022 4:13 PM
*To:* travis.m...@mfpdesign.com
*Cc:* sprinklerforum@lists.firesprinkler.org
*Subject:* [EXTERNAL] [Sprinklerforum] Re: Velocity - Rant



It's because they have velocity limits when sizing heating and water lines
and can't wrap their heads around sprinkler hydraulics.

when you have constant water flow through piping, high velocity wears the
pipe out faster, somehow they translate that to sprinkler pipe failure even
though sprinkler pipe rarely even sees any water flow!



Thanks



Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

br...@proudline.ca

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca
<https://urldefense.com/v3/__http:/www.proudline.ca/__;!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05NMb4e_4w$>









On Mon, Mar 14, 2022 at 1:50 PM <travis.m...@mfpdesign.com> wrote:

Does anyone have any idea where these engineers come up with the velocity
limits?  We have one that they are requiring a 10 PSI margin (not an issue
since AHJ requires 20%), but also limiting velocity to FOURTEEN fps.  There
has never been a limit in NFPA 13.  The velocity that we determine is only
based on a demand calc.  The water supply doesn’t know to reduce flow so
that a 10 psi margin is maintained.  If a single sprinkler activates, that
1” arm over is going to see far greater than 14 fps.



It really just baffles me how this criteria has become so ingrained in the
engineering culture.



Please rate our customer service
<https://urldefense.com/v3/__https:/survey.medallia.com/?emailsignature&fc=3539&bg=Fire*20and*20Fabrication__;JSU!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05PqkrhoUQ$>



*Travis Mack, CFPS, CWBSP, RME-G, COC, SET*

*Senior Engineering Manager*

*MFP Design*

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com

www.mfpdesign.com
<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!XuefiEhzuSpMkE5hwQfrMaq2esN89q-FRGseCr912x9x3M0x79mcWA0V05Muei1aEQ$>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to