Doesn't 13-13 25.2.1.6 exempt "Just you [sic] basic arm-over relocates."
from a hydrostatic test above system working pressure?
Ron Greenman
rongreen...@gmail.com
253.576.9700
The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, a
NFPA 13 – 2013 ed
We have a multi-tenant building that is entirely fed off one dry system.
We are doing some work on in one tenant. Just you basic arm-over
relocates. The AHJ wants us to hydrostatic test and air test the entire
building. Since we can’t isolate the area of work we would be res