Fire dept. connection

2017-03-29 Thread Lévis Blanchet
Concerning FDC installation like a 2-1/2’’ siamese connection Y-pattern, is there any official reference pertaining to orientation requirement that enforced the positioning on an horizontal plan? Lévis Blanchet Représentant technique Technical Representative lblanc...@vikingfire.ca

Re: Fire dept. connection

2017-03-29 Thread fpdcdesign
Most of the time I include a note to coordinate location with the local AHJ Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-553-3553 (tel:860-553-3553) (fax) 860-608-4559 (tel:860-608-4559) (cell)

RE: Fire dept. connection

2017-03-29 Thread Hinson, Ryan
-Based Systems Layout From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of fpdcdes...@gmail.com Sent: Wednesday, March 29, 2017 9:36 AM To: Sprinklerforum Subject: Re: Fire dept. connection Most of the time I include a note to coordinate location with the loc

Re: Fire dept. connection

2017-03-29 Thread Forest Wilson
Well, the internal swing check will not function peroperly in a vertical position On Wed, Mar 29, 2017 at 7:02 AM, Lévis Blanchet wrote: > Concerning FDC installation like a 2-1/2’’ siamese connection Y-pattern, > > is there any official reference pertaining to orientation requirement that > enf

Re: Fire dept. connection

2017-03-30 Thread Roland Huggins
I never noticed such aa requirement but never looked. Keep in mind access (not placement of the device but usability when the FD is hooking up) will be negatively affected. SO a bad idea even on a good day. Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. D