Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread å . . . . . . .
Brad: Freakonomics says, "name choice had no statistical influence in their evaluations of 'success' within a population. " That means people can call me "whatever," as long as we work together at getting the designs better. Don't put much truck in shame, but a spell checker is a worthwhile ende

Re: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread bcasterline
beside myself with... shame-- i mispelled your good name.. please forgive me scot. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread bcasterline
na Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... .... Sent: Tuesday, January 15, 2013 1:38 PM To: SprinklerFORUM@firesprinkler.org Subject

Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread å . . . . . . .
Drive > Severna Park, MD 21146-1904 > 410-544-3620 > 410-544-3032 FAX > 412-400-6528 Cell > > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... .... > Sent: Tuesday, January 15, 2013

RE: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread Bill Brooks
ailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... Sent: Tuesday, January 15, 2013 1:38 PM To: SprinklerFORUM@firesprinkler.org Subject: Maximum in-rack sprinkler spacing - plastic over 25ft Wayne: You make a good point. Per NFPA 13 in-rack sprinkler layouts, I don't pe

Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread å . . . . . . .
Wayne: You make a good point. Per NFPA 13 in-rack sprinkler layouts, I don't perceive that a gap between pallets constitutes a formal transverse flue. I think the transverse flue is formed by the steel column of the racking structure. Wayne, you are correct in that 2007 NPFA 13 Figure 17.3.1.

RE: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread Dewayne Martinez
esday, January 15, 2013 4:59 AM To: sprinklerforum@firesprinkler.org Subject: Maximum in-rack sprinkler spacing - plastic over 25ft Dewayne: I think it is an intention to put a in-rack sprinkler in every transverse flue (regardless of whether all in-rack sprinklers be at the same level of racking a

Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread å . . . . . . .
Dewayne: I think it is an intention to put a in-rack sprinkler in every transverse flue (regardless of whether all in-rack sprinklers be at the same level of racking as its nearest neighbor in-rack sprinklers). Transverse flues are very important to getting water down to the fire and for using

Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-14 Thread Dewayne Martinez
NFPA 13 (07ed) There is no maximum horizontal spacing shown on the figures specified in 17.3.1.2.1(a-c). For figure 17.3.1.2.1(a) does this mean that sprinklers must be placed horizontally at every other transvers flue space or since each pallet load is a cube measuring 4 to 5 ft the sprinklers