Brad:
Freakonomics says, "name choice had no statistical influence in their
evaluations of 'success' within a population. " That means people can call
me "whatever," as long as we work together at getting the designs better.
Don't put much truck in shame, but a spell checker is a worthwhile ende
beside myself with...
shame-- i mispelled your good name..
please forgive me scot.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
na Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... ....
Sent: Tuesday, January 15, 2013 1:38 PM
To: SprinklerFORUM@firesprinkler.org
Subject
Drive
> Severna Park, MD 21146-1904
> 410-544-3620
> 410-544-3032 FAX
> 412-400-6528 Cell
>
> -Original Message-
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... ....
> Sent: Tuesday, January 15, 2013
ailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å...
Sent: Tuesday, January 15, 2013 1:38 PM
To: SprinklerFORUM@firesprinkler.org
Subject: Maximum in-rack sprinkler spacing - plastic over 25ft
Wayne:
You make a good point.
Per NFPA 13 in-rack sprinkler layouts, I don't pe
Wayne:
You make a good point.
Per NFPA 13 in-rack sprinkler layouts, I don't perceive that a gap between
pallets constitutes a formal transverse flue. I think the transverse flue is
formed by the steel column of the racking structure.
Wayne, you are correct in that 2007 NPFA 13 Figure 17.3.1.
esday, January 15, 2013 4:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Maximum in-rack sprinkler spacing - plastic over 25ft
Dewayne:
I think it is an intention to put a in-rack sprinkler in every transverse flue
(regardless of whether all in-rack sprinklers be at the same level of
racking a
Dewayne:
I think it is an intention to put a in-rack sprinkler in every transverse
flue (regardless of whether all in-rack sprinklers be at the same level of
racking as its nearest neighbor in-rack sprinklers). Transverse flues are
very important to getting water down to the fire and for using
NFPA 13 (07ed)
There is no maximum horizontal spacing shown on the figures specified in
17.3.1.2.1(a-c). For figure 17.3.1.2.1(a) does this mean that
sprinklers must be placed horizontally
at every other transvers flue space or since each pallet load is a cube
measuring 4 to 5 ft the sprinklers