Subject: Re: NFPA 13R & NFPA 14 - (flow rates)
But domestic demand is added at the split with domestic and fire. The domestic
wouldn’t flow through standpipes.
It would have to be some crazy accessory use.
Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Engineering Man
February 6, 2021 2:27:55 PM
To: 'Jose Anibal Castillo' ;
sprinklerforum@lists.firesprinkler.org
; st...@protectiondesign.com
; sbi...@wenteplumbing.com
Cc: d...@engfirepro.com
Subject: RE: NFPA 13R & NFPA 14 - (flow rates)
I suspect that requirement is due more to the Domestic Demand
nal Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo
> Subje
..."
>
>
> Today's Topics:
>
>1. RE: NFPA 13R & NFPA 14 (Steve Leyton)
>2. RE: Existing Dry System (Chris Dorn)
>3. Re: NFPA 13R & NFPA 14 (Skyler Bilbo)
>4. Re: Existing Dry System (Skyler Bilbo)
>5. Slopes / Storage / UFC 3-600-01 change
org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases
orum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Jose Anibal Castillo via Sprinklerforum
Sent: Thursday, February 04, 2021 7:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Jose Anibal Castillo
Subject: NFPA 13R & NFPA 14
In section 7.10.1.3.1.1 of the nfpa 14, 201
Jose Anibal Castillo via Sprinklerforum
> Sent: Thursday, February 4, 2021 10:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo
> Subject: NFPA 13R & NFPA 14
>
> CAUTION: This email originated from outside of the organization. Do no
via Sprinklerforum
Sent: Thursday, February 4, 2021 10:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Jose Anibal Castillo
Subject: NFPA 13R & NFPA 14
CAUTION: This email originated from outside of the organization. Do not click
links or open attachments unless you can confirm the se
13R & NFPA 14
In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R
system demand is higher than the standpipe demand it is supposed to be chosen
the higher demand.
Is it even possible to have a residential sprinkler system with a higher demand
than the stand
In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R
system demand is higher than the standpipe demand it is supposed to be
chosen the higher demand.
Is it even possible to have a residential sprinkler system with a higher
demand than the standpipe?
Regards
José A.