Re: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
Yes sir - it was added for the 2016 edition of NFPA 13 and remained the same for the 2019 edition. Problem solved. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firespri

RE: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Kyle.Montgomery via Sprinklerforum