Original Message-
From: Sprinklerforum On Behalf
Of John Denhardt via Sprinklerforum
Sent: Monday, September 13, 2021 12:15 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Denhardt
Subject: Re: Fire Pump Room Sprinkler Classification
I understand NFPA 37 (18edt), section 11.4.5.1 state
forum On
>> Behalf Of John Denhardt via Sprinklerforum
>> Sent: Monday, September 13, 2021 11:55 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: John Denhardt ; Prahl, Craig/GVL <
>> craig.pr...@jacobs.com>; James Crawford
>> Subject: Re: Fire Pump Room
alf Of John Denhardt via Sprinklerforum
> Sent: Monday, September 13, 2021 11:55 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: John Denhardt ; Prahl, Craig/GVL <
> craig.pr...@jacobs.com>; James Crawford
> Subject: Re: Fire Pump Room Sprinkler Classification
>
> Language w
Subject: Re: Fire Pump Room Sprinkler Classification
Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven fire
pump system.
NFPA 20 - 2019 edition
4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump buildings
or rooms enclosing diesel engine pump drivers
Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven
fire pump system.
NFPA 20 - 2019 edition
4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump
buildings or rooms enclosing diesel engine pump drivers and day tanks shall
be protected with an automatic
NFPA 20 is clear that the pump room is to be protected per EH2. By
definition of EH2, the presence of the diesel fuel makes it EH2. See
4.14.1.3
Bob Caputo, CFPS
President
American Fire Sprinkler Association
-Original Message-
From: Sprinklerforum On
Behalf Of James Crawford via
lHhABSexWY%3D=0>
From: Sprinklerforum On Behalf
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Monday, September 13, 2021 10:49 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl, Craig/GVL ; James Crawford
Subject: RE: Fire Pump Room Sprinkler Classification
If you look at the defi
If you look at the definitions in NFPA 13 of the various occupancies, the
presence of diesel fuel (combustible liquid) would dictate an EH2.
With electric pumps OH1 or OH2 would be fine.
Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
craig.pr...@jacobs.com | www.jacobs.com
1041 East