RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Matthew J Willis via Sprinklerforum
Original Message- From: Sprinklerforum On Behalf Of John Denhardt via Sprinklerforum Sent: Monday, September 13, 2021 12:15 PM To: sprinklerforum@lists.firesprinkler.org Cc: John Denhardt Subject: Re: Fire Pump Room Sprinkler Classification I understand NFPA 37 (18edt), section 11.4.5.1 state

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
forum On >> Behalf Of John Denhardt via Sprinklerforum >> Sent: Monday, September 13, 2021 11:55 AM >> To: sprinklerforum@lists.firesprinkler.org >> Cc: John Denhardt ; Prahl, Craig/GVL < >> craig.pr...@jacobs.com>; James Crawford >> Subject: Re: Fire Pump Room

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
alf Of John Denhardt via Sprinklerforum > Sent: Monday, September 13, 2021 11:55 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: John Denhardt ; Prahl, Craig/GVL < > craig.pr...@jacobs.com>; James Crawford > Subject: Re: Fire Pump Room Sprinkler Classification > > Language w

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Matthew J Willis via Sprinklerforum
Subject: Re: Fire Pump Room Sprinkler Classification Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven fire pump system. NFPA 20 - 2019 edition 4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump buildings or rooms enclosing diesel engine pump drivers

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven fire pump system. NFPA 20 - 2019 edition 4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump buildings or rooms enclosing diesel engine pump drivers and day tanks shall be protected with an automatic

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Bob Caputo via Sprinklerforum
NFPA 20 is clear that the pump room is to be protected per EH2. By definition of EH2, the presence of the diesel fuel makes it EH2. See 4.14.1.3 Bob Caputo, CFPS President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of James Crawford via

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Travis Mack via Sprinklerforum
lHhABSexWY%3D=0> From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Monday, September 13, 2021 10:49 AM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig/GVL ; James Crawford Subject: RE: Fire Pump Room Sprinkler Classification If you look at the defi

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Prahl, Craig/GVL via Sprinklerforum
If you look at the definitions in NFPA 13 of the various occupancies, the presence of diesel fuel (combustible liquid) would dictate an EH2. With electric pumps OH1 or OH2 would be fine. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East