> It depends on the rating of
AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sleeve requirements
It depends on the rating of the wall and the type of fire caulking you use, 1
and 2 hour rated wall you do not need a sleeve but if you are going thru a 4
hour wall you need to use a sleeve.
Richard Carr, SET
Branch
It depends on the rating of the wall and the type of fire caulking you use, 1
and 2 hour rated wall you do not need a sleeve but if you are going thru a 4
hour wall you need to use a sleeve.
Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@
The requirements are in the particular fire-stop assemblies; some are listed
with sleeves, some without sleeves.