Re: Sleeve requirements

2016-08-11 Thread rongreenman .
> > *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] *On Behalf Of *Richard Carr > *Sent:* Thursday, August 11, 2016 10:26 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Sleeve requirements > > > > It depends on the rating of

RE: Sleeve requirements

2016-08-11 Thread Steve Leyton
AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Sleeve requirements It depends on the rating of the wall and the type of fire caulking you use, 1 and 2 hour rated wall you do not need a sleeve but if you are going thru a 4 hour wall you need to use a sleeve. Richard Carr, SET Branch

RE: Sleeve requirements

2016-08-11 Thread Richard Carr
It depends on the rating of the wall and the type of fire caulking you use, 1 and 2 hour rated wall you do not need a sleeve but if you are going thru a 4 hour wall you need to use a sleeve. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 rc...@

RE: Sleeve requirements

2016-08-11 Thread Brad Casterline
The requirements are in the particular fire-stop assemblies; some are listed with sleeves, some without sleeves. b _ From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Williams Sent: Thursday, August 11, 2016 11:22 AM To: sprinklerforum@l