To my understanding: Yes and yes.
On Thu, Jul 21, 2016 at 9:31 AM, Todd Williams wrote:
> Section 11.1.2 permits a higher hazard area within a larger space to be
> protected with sprinklers over the hazard and 15 ft beyond. Since nothing
> is stated, I assume this can be done with a dry system.
The total remote area should be increased by 30% but no increase needed for the
15 ft.