RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
rinklerforum-boun...@lists.firesprinkler.org] On Behalf Of JD Gamble Sent: Thursday, March 29, 2018 4:10 PM To: sprinklerforum@lists.firesprinkler.org; sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] [EXTERNAL] Sorry. This is F-2 <12%

Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
klerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] I’m sure the AHJ would balk at considering a restaurant as an F-1. So it sounds like there are several issues. First the architect needs to revisit and verify the separation requirements between an F-1 and an A

RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
8 3:14 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Do the whole building is F-1 with an open restaurant inside? On Thu, Mar 29, 2018 at 12:05 PM JD Gamble mailto:jgam...@lssofsheridan.com>> wrote: Yes. F-1 in the basement wi

Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Is the 900 sq. ft. opening to accommodate the height of the tanks. The tanks and their associated piping and controls are visible on the same level as the seating around the tanks? Is 1st f

Re: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Ron Greenman
Get Outlook for iOS <https://aka.ms/o0ukef> > -- > *From:* Sprinklerforum > on behalf of Prahl, Craig/GVL > *Sent:* Thursday, March 29, 2018 12:25:52 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Vertical Opening [EXTERNAL] [EX

RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
nt: Thursday, March 29, 2018 3:06 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Yes. F-1 in the basement with a through floor opening for the tanks. Seating on the 1st around the tanks. Main level is restaurant with restaurant seating. Get

Re: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
Sent: Thursday, March 29, 2018 12:25:52 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] [EXTERNAL] So, is the A occupancy on the first floor and F-1 is the second floor? Is there seating on the first level and the opening is so you can see the equipment on the

RE: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
erforum-boun...@lists.firesprinkler.org] On Behalf Of JD Gamble Sent: Thursday, March 29, 2018 1:55 PM To: sprinklerforum@lists.firesprinkler.org; sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] Restaurant/ Brewery No ratings, Something about F1 to A n