Re: Structural Load

2020-06-04 Thread BRUCE VERHEI via Sprinklerforum
Skyler We used to see WSRB or FM jobs with 0.39 gpm/sf over 5,600 sf as standard warehouse design. Based on previous engineers comments we normally said structural plans had to reserve 2.5 lbs/sf for sprinklers where they were deferred permit, which was always. 2.5 was conservative. Sometimes

Re: Structural Load

2020-06-03 Thread Skyler Bilbo via Sprinklerforum
The structure needs to support a larger point load (with a very complex explanation, it probably does). Otherwise, if a guy working on the roof were to stand on one foot, the structure could potentially collapse. Structural engineering calculations are extremely complex (I would say more so than o

RE: Structural Load

2020-06-03 Thread Steve Leyton via Sprinklerforum
...@lists.firesprinkler.org] On Behalf Of Ron Greenman via Sprinklerforum Sent: Wednesday, June 03, 2020 9:41 AM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Structural Load And remember the building does not belong to you and it is NOT your responsibility to come up with a

Re: Structural Load

2020-06-03 Thread Ron Greenman via Sprinklerforum
And remember the building does not belong to you and it is NOT your responsibility to come up with a solution. The owner, via his representatives (the GC, the structural engineer, and ultimately, the architect) is responsible for building a code-compliant building that includes supporting any live

Re: Structural Load

2020-06-03 Thread John Denhardt via Sprinklerforum
I agree with Ken. I have been down this road before. The structure needs to support the piping plus 250 pounds at the point of hanging. If the structure can handle this load, then the structure has an issue. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Servic

Re: Structural Load

2020-06-03 Thread Parsley Consulting via Sprinklerforum
Jerry, Although I'm slightly unclear over what you're being told I would make sure that whoever is providing that information to you has read 9.2.1.3.1 of the '16 edition of -13: 9.2.1.3.1 Sprinkler piping shall be substantially supported from the building structure, *which must support

Re: Structural Load

2020-06-03 Thread cw bamford via Sprinklerforum
Building loads may use a different safety factor from the 2019 NFPA 13 table A.18.5.9 4" sch 1011.78 lbs/ft if hangers are every 10' that's 117.8 lbs at each hanger. hangers every 15' 177lbs. Sprinkler design safety factor is 5 times + 250 lbs they MAY design a 5 times dead load

Structural Load

2020-06-03 Thread Jerry Van Kolken via Sprinklerforum
I have a building where they are telling me the structural point loading on the framing less than 250lbs. (140lbs) Advice? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730