Thermal Barrier for Bathrooms

2014-05-15 Thread Chris Born
I'm looking for a quick sanity check. We are an A/E firm designing new college dormitories. These dorms typically contain four bedroom suites with two bathrooms in each suite. The 1987 edition of 2013 is applicable, and the bathrooms are less than 55 square feet. In order to omit sprinklers

RE: Thermal Barrier for Bathrooms

2014-05-15 Thread RFletcher
...@lists.firesprinkler.org] On Behalf Of Chris Born Sent: Thursday, May 15, 2014 2:18 PM To: sprinklerfo...@firesprinkler.org Subject: Thermal Barrier for Bathrooms I'm looking for a quick sanity check. We are an A/E firm designing new college dormitories. These dorms typically contain four bedroom suites wit

Re: Thermal Barrier for Bathrooms

2014-05-15 Thread Roland Huggins
That is my understanding (despite the fact that a door is not required to the adjacent room). Never said it ad to be logical. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On May

Re: Thermal Barrier for Bathrooms

2014-05-15 Thread John Drucker
Barrier for Bathrooms That is my understanding (despite the fact that a door is not required to the adjacent room). Never said it ad to be logical. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http

Re: Thermal Barrier for Bathrooms

2014-05-16 Thread Forest Wilson
On your project, I would send an RFI to the Architect and ask: Are the bathrooms thermal barrier as required by IBC ? On 5/15/2014 6:47 PM, Roland Huggins wrote: That is my understanding (despite the fact that a door is not required to the adjacent room). Never said it ad to be logical.

RE: Thermal Barrier for Bathrooms

2014-05-16 Thread Mark A. Sornsin, P.E.
-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Thursday, May 15, 2014 5:48 PM To: SprinklerFORUM Subject: Re: Thermal Barrier for Bathrooms That is my understanding (despite the fact that a door is not required to the adjacent room). Never said it ad to be lo

RE: Thermal Barrier for Bathrooms

2014-05-16 Thread RFletcher
...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Friday, May 16, 2014 8:49 AM To: sprinklerfo...@firesprinkler.org Subject: RE: Thermal Barrier for Bathrooms Roland, Isn't the concern that fire will spread to the unprotected concealed space, spreading heat and smoke to other par