September 25, 2018 3:14 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Re: Type V Construction & Hangers
There are several types of lightweight roof construction that I expected notes
about point loads imposed by sprinklers to be on
From: Sprinklerforum On
Behalf Of Steve Leyton
Sent: Tuesday, September 25, 2018 5:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Type V Construction & Hangers
Maybe so, but here's the thing: if you apply the seismic load factors (as
you're supposed to in the building code) to standard de
?
Matt
From: Sprinklerforum On Behalf
Of John Denhardt
Sent: Tuesday, September 25, 2018 6:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] Re: Type V Construction & Hangers
In one jurisdiction, it has been that way for over 20 years to require a
struct
2018 3:14 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Re: Type V Construction & Hangers
There are several types of lightweight roof construction that I expected notes
about point loads imposed by sprinklers to be on the str
rforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Re: Type V Construction & Hangers
There are several types of lightweight roof construction that I expected notes
about point loads imposed by sprinklers to be on the structural plans. Another
nklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Type V Construction & Hangers
I know you CA peeps do. I had just never run into it outside of CA.
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 8
esday, September 25, 2018 2:31 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Type V Construction & Hangers
>
> I know you CA peeps do. I had just never run into it outside of CA.
>
>
>
> Travis Mack, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
>
ber 25, 2018 2:31 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Type V Construction & Hangers
I know you CA peeps do. I had just never run into it outside of CA.
[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
e
Of MFP Design, LLC
Sent: Tuesday, September 25, 2018 4:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Type V Construction & Hangers
Has anyone run into situations where the AHJ is requiring the structural
engineer on a project to provide a sealed criteria letter for the pro
8 5:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Type V Construction & Hangers
Has anyone run into situations where the AHJ is requiring the structural
engineer on a project to provide a sealed criteria letter for the project
indicating the maximum hanger spacing based on
i%2FhbeCbHNRijI%3D=0>
https://www.linkedin.com/in/travismack
"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."
From: Sprinklerforum On
Behalf Of Steve Leyton
Sent: Tuesday, September 25, 2018 2:30 PM
To: sprinklerforum@lists.firesprink
All the time bruddah.
SML
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Tuesday, September 25, 2018 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Type V Construction & Hangers
Has anyone run into situations w
Has anyone run into situations where the AHJ is requiring the structural
engineer on a project to provide a sealed criteria letter for the project
indicating the maximum hanger spacing based on pipe size and structural
member? We are seeing one local jurisdiction start to require this.
13 matches