2019-06-07 Thread Roland Huggins
rotected as a “localized exposed combustible” per >> NFPA 13 2016 8.15.1.5? >> >> >> >> Matt >> >> >> >> From: Sprinklerforum > <mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of JD >> Gamble >>

Re: Vertical Opening

2019-06-07 Thread Roland Huggins
otected as a “localized exposed combustible” per > NFPA 13 2016 8.15.1.5? > > > > Matt > > > > From: Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of JD > Gamble > Sent: Tuesday, June 04, 2019 8:25 AM > To: spr

Re: Vertical Opening

2019-06-04 Thread Jeff Normand
Matt > > > > *From:* Sprinklerforum *On > Behalf Of *JD Gamble > *Sent:* Tuesday, June 04, 2019 8:25 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Vertical Opening > > > > John, > > > > I am interested in the thoughts on this a

RE: Vertical Opening

2019-06-04 Thread Matt Grise
Any chance this could be protected as a "localized exposed combustible" per NFPA 13 2016 8.15.1.5? Matt From: Sprinklerforum On Behalf Of JD Gamble Sent: Tuesday, June 04, 2019 8:25 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening John, I am interes

RE: Vertical Opening

2019-06-04 Thread John Irwin
Protection "The bitterness of poor quality remains long after the sweetness of low price is forgotten." - Benjamin Franklin From: Sprinklerforum On Behalf Of JD Gamble Sent: Tuesday, June 4, 2019 9:25 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening John, I am

RE: Vertical Opening

2019-06-04 Thread JD Gamble
JD From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: Tuesday, June 4, 2019 5:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: Vertical Opening Client spring these openings on us just before final. Client says the building department OK&#x

Vertical Opening

2019-06-04 Thread John Irwin
Client spring these openings on us just before final. Client says the building department OK'd the new plan so we should be good to go. I know I need upright protection up there, but can't find the exact references to make my case. Anyone? [A picture containing indoor, floor, building, ground

RE: vertical opening

2019-03-25 Thread Prahl, Craig/GVL
cobs.com> | www.jacobs.com<http://www.jacobs.com/> From: Sprinklerforum On Behalf Of Easter, Tim (Contractor) Sent: Friday, March 22, 2019 9:53 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] vertical opening We have cylindrical duct passing thru an opening through three flo

Re: vertical opening

2019-03-22 Thread Fpdcdesign
It seems sealing it would be a .lot cheaper than a 3500 gpm pump Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Mar 22, 2019 at 9:53 AM, (mailto:tim.eas...@holston-aap.c

vertical opening

2019-03-22 Thread Easter, Tim (Contractor)
We have cylindrical duct passing thru an opening through three floors, that is not sealed or enclosed. This duct is used for industrial process. Each floor is protected by a deluge system. Is there a requirement in NFPA 13 or 15 that requires the hydraulically design area to include all 3 floors?

Re: Vertical Opening

2018-03-30 Thread bcasterline
Quoting JD Gamble : "... a draft stop is not a viable solution due to head room "... my fear is these things being left open in a fire situation". When I got into fire modeling 12 years ago I did an activation comparison with and without a draft stop. I was curious to see how much longer

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread AKS-Gmail-IMAP
it meant until reading it as referring to whenever sprinkler protection in general provides the alternative to the vertical opening shaft enclosure. The 8.15.4.1 statement does not qualify the “sprinkler protection” nor the alternative means. In other words the bolded and underlined part of

RE: Vertical Opening [EXTERNAL]

2018-03-29 Thread Kyle.Montgomery
8.15.4.1 General. Unless the requirements of 8.15.4.4 are met, where moving stairways, stairways, staircases, or similar floor openings are unenclosed and where sprinkler protection is serving as the alternative to enclosure of the vertical opening, the floor openings involved shall be

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread bcasterline
ly for this opening? Get Outlook for iOS<https://aka.ms/o0ukef> From: Sprinklerforum on behalf of bcasterl...@fsc-inc.com Sent: Thursday, March 29, 2018 2:13:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] You

RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
rinklerforum-boun...@lists.firesprinkler.org] On Behalf Of JD Gamble Sent: Thursday, March 29, 2018 4:10 PM To: sprinklerforum@lists.firesprinkler.org; sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] [EXTERNAL] Sorry. This is F-2 <12%

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread JD Gamble
rinkler.org Subject: Re: Vertical Opening [EXTERNAL] You should probably confirm it with every one J.D. but it seems to me if separation (protection, enclosure) is not required there would be no reason to use sprinklers as an alernative for providing that separation. It's been ten years since I last

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread bcasterline
behalf of Prahl, Craig/GVL Sent: Thursday, March 29, 2018 11:52:01 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] Is this like an atrium? What's the occupancy? Any fire rating of floor/ceiling between levels? Craig Prahl | JACOBS | Fire Pr

Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
Sorry. This is F-2 <12% alcohol. So no separation issue. But still a vertical opening issue. Get Outlook for iOS<https://aka.ms/o0ukef> From: Sprinklerforum on behalf of Prahl, Craig/GVL Sent: Thursday, March 29, 2018 1:56:54 PM To: sprin

RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
8 3:14 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Do the whole building is F-1 with an open restaurant inside? On Thu, Mar 29, 2018 at 12:05 PM JD Gamble mailto:jgam...@lssofsheridan.com>> wrote: Yes. F-1 in the basement wi

Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Is the 900 sq. ft. opening to accommodate the height of the tanks. The tanks and their associated piping and controls are visible on the same level as the seating around the tanks? Is 1st f

Re: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Ron Greenman
Get Outlook for iOS <https://aka.ms/o0ukef> > -- > *From:* Sprinklerforum > on behalf of Prahl, Craig/GVL > *Sent:* Thursday, March 29, 2018 12:25:52 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Vertical Opening [EXTERNAL] [EX

RE: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
nt: Thursday, March 29, 2018 3:06 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] [EXTERNAL] Yes. F-1 in the basement with a through floor opening for the tanks. Seating on the 1st around the tanks. Main level is restaurant with restaurant seating. Get

Re: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread JD Gamble
Sent: Thursday, March 29, 2018 12:25:52 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] [EXTERNAL] So, is the A occupancy on the first floor and F-1 is the second floor? Is there seating on the first level and the opening is so you can see the equipment on the

RE: Vertical Opening [EXTERNAL] [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
erforum-boun...@lists.firesprinkler.org] On Behalf Of JD Gamble Sent: Thursday, March 29, 2018 1:55 PM To: sprinklerforum@lists.firesprinkler.org; sprinklerforum@lists.firesprinkler.org Subject: Re: Vertical Opening [EXTERNAL] [EXTERNAL] Restaurant/ Brewery No ratings, Something about F1 to A n

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread JD Gamble
018 11:52:01 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Vertical Opening [EXTERNAL] Is this like an atrium? What's the occupancy? Any fire rating of floor/ceiling between levels? Craig Prahl | JACOBS | Fire Protection | Greenville SC | 864.676.5252 | craig.pr.

RE: Vertical Opening [EXTERNAL]

2018-03-29 Thread Prahl, Craig/GVL
Is this like an atrium? What's the occupancy? Any fire rating of floor/ceiling between levels? Craig Prahl | JACOBS | Fire Protection | Greenville SC | 864.676.5252 | craig.pr...@ch2m.com | www.jacobs.com Quoting JD Gamble : > I have a situation where we have 900sq.ft. vertical

Re: Vertical Opening

2018-03-29 Thread bcasterline
Is the opening required to be 'protected' from a building code standpoint? If it is, Then you look at the sprinkler rules, such as less than 1000 s.f. I hope this makes sense. Brad. Quoting JD Gamble : I have a situation where we have 900sq.ft. vertical opening communicating b

Vertical Opening

2018-03-29 Thread JD Gamble
I have a situation where we have 900sq.ft. vertical opening communicating between two floors where a draft stop is not a viable solution due to head room clearance. The design team isn't sure if or how to protect it? Thoughts? Options? It's a Light Hazard - Ord Hazard occ. The ide

RE: Closely spaced heads at vertical opening

2016-06-13 Thread Tim Stone
PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Closely spaced heads at vertical opening Don't water curtains require a deluge approach. I'm not sure what that configuration shown in 13 is supposed to do but certainly not a full curtain around the opening. On Monday, June 13,

Re: Closely spaced heads at vertical opening

2016-06-13 Thread rongreenman
ler.org > ] > *On Behalf Of *Matt Grise > *Sent:* Monday, June 13, 2016 12:53 PM > *To:* sprinklerforum@lists.firesprinkler.org > > *Subject:* RE: Closely spaced heads at vertical opening > > > > These would be mounted in the draftstop (a boxed out steel I-beam) pointed &g

RE: Closely spaced heads at vertical opening

2016-06-13 Thread Tim Stone
PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Closely spaced heads at vertical opening These would be mounted in the draftstop (a boxed out steel I-beam) pointed away from the opening. I am not clear on the intent of the design. The closely spaced sidewall sprinklers would cover more

RE: Closely spaced heads at vertical opening

2016-06-13 Thread Matt Grise
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Michael Hill Sent: Monday, June 13, 2016 11:37 AM To: Subject: Re: Closely spaced heads at vertical opening Sidewalks pointed at the draft stop? I thought part of the reasoning was to have water hit the draft

Re: Closely spaced heads at vertical opening

2016-06-13 Thread Michael Hill
Sidewalks pointed at the draft stop? I thought part of the reasoning was to have water hit the draft stop and create a wall of water. Mike Hill Sent from my iPhone > On Jun 13, 2016, at 12:18 PM, Matt Grise wrote: > > I have an application where an open stairway will require closely spaced >

Closely spaced heads at vertical opening

2016-06-13 Thread Matt Grise
I have an application where an open stairway will require closely spaced heads and draft stopping. The construction of the opening lends itself to the use of sidewall sprinklers set in the draftstop to serve as the closely spaced heads. Is there anything that prohibits this? In reviewing the han

Re: vertical opening

2008-08-05 Thread Roland Huggins
This is more a vertical opening into an otherwise concealed space. It's worth noting that the TC as accepted effectively 2 rows of sprinklers at such locations instead of the entire space. This will most likely be refined slight at the ROC since it currently is based on a percenta