Just right a condition rule which allows you to parse the varbind string for
what your looking for. It's a lot easier to setup then is sounds..here's some
code that's similar. I have one (1) varbind that passes like 15 different
values....here's what I did:
0xfff00015 E 0 R CA.EventCondition, "(regexp({v 1}, {S \"Cleared:Load On
Battery \"}))" , "0xfff00017 -:-","(regexp({v 1}, {S \"Cleared:Bad Input
Frequency\"}))"
, "0xfff00000 -:-","(regexp({v 1}, {S \"Cleared:Bypass Input
Voltage/Frequency Fault\"}))" , "0xfff00000 -:-","(regexp({v 1}, {S
\"Cleared:Load On Battery\"}))
" , "0xfff00018 -:-","(regexp({v 1}, {S
\"Cleared:Battery Test Failed\"}))" , "0xfff00019 -:-","(regexp({v 1}, {S
\"Cleared:Load On Bypass\"}))" , "0xfff0001a -:-","(regexp({v 1}, {S \"Cleared:
Battery Test Failed\"}))" , "0xfff0001b -:-","(regexp({v 1}, {S \"Cleared:Low
Battery\"}))" , "0xfff0001c -:-","(regexp({v 1},{S \"Cleared:Input Under
Voltage\"}))" , "0xfff0001f -:-","(regexp({v 1}, {S \"System Return to
Normal\"}))" , "0xfff00020 -:-","(regexp({v 1}, {S \"Cleared:Input Over
Voltage\"}))" , "0xfff00029 -:-"
The "v 1" is the varbind that passess all these different values we need to
serach for our autoclears. Once a match is made is generares a uniuque alarm
who's sole purpose is to clear the outstanding corresponding alarm. For
debugging purposes any time this varbind is sent I have a generic event that
passes the info in the trap in case I receive a new varbind value I have never
seen.
HTH...
Andy
From: Cutting, Jeremiah [mailto:[email protected]]
Sent: Friday, July 29, 2011 1:51 PM
To: spectrum
Subject: [spectrum] help with clearing trap
Running Spectrum 9.1. I need some help with figuring out how to create a
clearing event for an alarm. I have two traps (separate oids) from a device,
an up and a down trap. Each trap contains two varbinds, one of which is
useable to clear the down trap (the other just contains the device IP). The
problem is that the string in the varbinds don't quite match. So for example:
DOWN trap
Varbind1 = blahblahblah_DOWN
UP trap
Varbind1 = blahblahblah_UP
The blahblahblah always matches, it's just the addition of _UP and _DOWN that
is different. So setting up a simple clear won't work, and I can't have the UP
alarm clear all alarms for the device because of the nature of the alarm. Any
suggestions?