There have bee occasions where we have run into the "other" brands of
composite joist and have contacted there tech people.  Surprisingly, they
have referenced us back to Truss Joist McMillan data and simply instructed
us to "Do what they show".  Don't know if this is good or bad, but it's been
the reality.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 14, 2006 10:12 AM
To: [email protected]
Subject: Re: Hanging off TGI's

TJI has become a generic name for all web type joist, but they vary greatly 
in their engineering support from Mfg. to Mfg. If indeed you are using the 
"Truss Joist McMillan" TJI or the (Wearhouser) TJI your in luck. If its 
another brand such as BCI or Louisiana Pacific info is harder to get.
The method we have used in the past and had approved by the TJI engineering 
staff is to install two pieces of plywood to reinforce the web as per their 
bearing point detail (Nails and Construction adhesive) then use the Sammy 
side winder through the plywood reinforcement to hang from this will allow 
your hanger to hang perpendicular or as a pendent for slope roof/ceiling 
structures. Please note that while TJI only requires 3/4" plywood, you'll 
need to use 7/8" to keep your 2" Sammy screw in the wood, and not sticking 
out the other side.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to