You bet, to follow

John



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Lindner,
Richard
Sent: Wednesday, November 15, 2006 12:29 PM
To: [email protected]
Subject: RE: Elevator Recall

John,

If you could provide the code references/year issued it would be
appreciated, especially the requirements for the smoke detectors
requirements in hoistways.

Richard


 
Richard K. Lindner
Plumbing Senior Designer
Morris, Johnson & Associates, Inc.
 
611 Industrial Way West
Eatontown, New Jersey  07724
P:  732-380-1100 ext. 4186  |  F:  732-380-1111
[EMAIL PROTECTED]
www.morrisjohnson.com
-----Original Message-----

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of John
Drucker
Sent: Wednesday, November 15, 2006 9:07 AM
To: [email protected]
Subject: RE: Elevator Recall


George,

Sprinklers may be omitted in the hoistway if a) hoistway is non
combustible, b) car is non combustible construction and c) Hydraulic
fluids (if hydraulic elevator) are non-combustible.  However there is no
such exception for the elevator machine room which must be sprinklered
hence the need for shunt trip due to this sprinkler.

Phase I Recall is always required, the 25ft travel rule eliminated. If
sprinklers are omitted from the hoistway due to the conditions listed
above then a smoke detector is not required and actually prohibited at
the top of the hoistway.  However  a smoke detector configured for phase
I recall is required at each lobby and the elevator machine room.

Let me know if you need the code references, I can provide them when I
get back in.

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Geoff
Dyce
Sent: Wednesday, November 15, 2006 8:57 AM
To: [email protected]
Subject: Elevator Recall

Roland or someone....I need your input re: a question put to me
yesterday.
When a building has an elevator, when would an elevator recall and shunt
be
required??  The building is totally sprinklered, elevator is per ASME
A17.1
with no sprks at the top and bottom of the shaft.  I say always and
others
say I'm wrong.  What do you say??


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to