By their listing and your use, the EC heads are standard response.  To
be consistent, you would install a standard response sprinkler in the
bump-outs.

In reality, I can't imagine there would be a performance issue using the
QR heads as you described in lieu of SR.  But reality doesn't
necessarily count if you're following the letter of "the codes."

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jim
Zimmerman
Sent: Tuesday, November 28, 2006 8:24 AM
To: [email protected]
Subject: Ordinary Hazard I areas with Extended Coverage Heads &
StandardHeads

In a garage (parking in the basement of senior housing) I am using
extended coverage heads (Viking ELO's). Since the garage is OH1 the EC
heads are listed as Standard Response (per the tech data), even though
the bulb is a QR bulb. In some areas I need to add a head to pick up a
small corner or bump-out so I am using a standard 3/4" 8.0K upright.
What response will this head be? Going by the listing of the EC heads
these heads should be SR. But the EC heads have a QR bulb so should I
use 3/4" QR 8.0K Uprights for the bump-outs?
 