Can't answer any of those questions Scot, but I'm waiting on a response from
FM and then it's going back to the engineer of record.
Russell
From: "å... ...." <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: [email protected]
Subject: Big Ass Fans
Date: Tue, 28 Nov 2006 20:41:42 +0000
how do you intend on notifying occupants in a
office of a fire in the general warehouse, without
an alarm? did you intend "smoke detection"
instead of "fire alarm". The one pull-station rule is
due to be (if not already) culled from the standard,
but this also could shut-down the fan.
remember to include up to 2 sprinklers from under
the obstruction in the hydraulic calc with the overhead.
Scot Deal
Excelsior Fire
On 11/28/06, Scott A. Futrell <[EMAIL PROTECTED]> wrote:
Since fire alarm systems are not desired or required in most of these
storage occupancies, the only fire alarm system that will shut down the
fans is the operation of the water flow switch on the sprinkler systems
and if that is delayed because of the fans, I fail to see how that helps
the situation, or should be allowed.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of hughes
rewis
Sent: Tuesday, November 28, 2006 7:14 AM
To: [email protected]
Subject: Big Ass Fans
Well, I dug a little deeper into my filing system and found the
documents
sent to me from the manufacturer. In it ESFR sprinklers are discussed.
In
capsulated form it states that the two issues are obstruction and air
velocity. First it says that the fans are shut down when the fire alarm
system responds to a fire situation. Air velocity is typically limited
to 5
ft/sec. It goes into great detail of test in several diffent senarios,
of
which I will not go into. Quite lenghty.
Though I'd pass this along.
Thanks,
Hughes
_________________________________________________________________
Stay up-to-date with your friends through the Windows Live Spaces
friends
list.
http://clk.atdmt.com/MSN/go/msnnkwsp0070000001msn/direct/01/?href=http:/
/spaces.live.com/spacesapi.aspx?wx_action=create&wx_url=/friends.aspx&mk
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_________________________________________________________________
Get FREE company branded e-mail accounts and business Web site from
Microsoft Office Live
http://clk.atdmt.com/MRT/go/mcrssaub0050001411mrt/direct/01/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum