They are pulled from the litany of allowances in 8.14.1.2 (02 ed) AND
one is from the restrictions on the 3000 sf remote area criteria of
chap 11 (I must confess I ASSUMED they were all from the 8.14.1.2
group). They are only in the 07 edition for chap 8.15.7 but their 02
ed locations are: 8.14.1.2.7 (filled with insulation) / 8.14.2.1.9
about over small rooms of 55 sf but it says canopies, roofs, or porte-
cocheres instead of rooms, and 11.2.3.1.8 (4)(b) which applies only
to SOLID wood joists and not composite joists.
Roland
On Nov 30, 2006, at 7:13 AM, Kathy Blair wrote:
Thank you very much for your reply and also for looking into
addresses this
with the committee for the 2007 edition. However, you keep
mentioning the
three old allowances and the AHJ is asking for those to be called
out. So I
hate to ask but could you please list those three allowances?
Thank you Roland,
Kathy