Jim,

Those conditions are similar to the definition of  "habitable attic" in
New Jersey, additionally the habitable attic cannot exceed 1/3 the area
of the floor below. Suppression would be required where provided.

John Drucker 
Fire Protection Subcode Official
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jim
Kettler
Sent: Monday, December 11, 2006 7:57 AM
To: [email protected]
Subject: RE: Attics in 13r and 13d

The attics were a big issue here given the larger size of many of the
homes.
We looked at the definition of "attic" and tried to match up the
specific
requirements. In the end, we created a rule of thumb - trying to
consider
all of the variables. Our rule of thumb is that sprinklers are required
if
the all three conditions are met: there are walk-up stairs, there is
flooring installed, and there is full headroom in the space. This has
worked
extremely well for us, though your mileage may vary.

Jim Kettler
Fire Marshal
Buckingham, PA




> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] Behalf Of
> Bob Knight
> Sent: Friday, December 01, 2006 04:01 PM
> To: [email protected]
> Subject: RE: Attics in 13r and 13d
>
>
> I remember this question from a couple of years back, and
> Roland gave an
> answer something to the affect, that unless the attic is to
> be used for
> habitation, it doesn't need sprinklered.  That is if you have
> a 13D system.
> It sounds like that from your description.  So, I guess the
> question should
> have first been asked, is this a 13D or 13R system?
>
> Bob Knight
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to