I would never be concerned from strictly a practical (not listing or NFPA
#13) point of view about a few inches in an open room with a heat pump. The
head that was activated was in a heater closet and the duct had a cut it in
that allowed the warm air to fill the room straight from the source with
nowhere for the air to escape. We have seen hundreds of diffusers closer
than even 12” that have been in operation for years without a problem. We
strive for 24” but the hvac guys often infringe on that space a little and
the local authorities have never had a problem with it.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andy Johnston
Sent: Wednesday, December 13, 2006 8:40 AM
To: [email protected]
Subject: RE: hot air flues

We are using 155° Res heads. The question is really the definition. We are
in the process of changing them to 175° because of a inch and a half. 24" to
the side of a hot air diffuser when both of us want to be in the middle of
the room. This causes a problem but not like having a head go off because
the heater came on.

Thank you for your attention.
Andy Johnston