I would never be concerned from strictly a practical (not listing or NFPA #13) point of view about a few inches in an open room with a heat pump. The head that was activated was in a heater closet and the duct had a cut it in that allowed the warm air to fill the room straight from the source with nowhere for the air to escape. We have seen hundreds of diffusers closer than even 12 that have been in operation for years without a problem. We strive for 24 but the hvac guys often infringe on that space a little and the local authorities have never had a problem with it. Greg
Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Andy Johnston Sent: Wednesday, December 13, 2006 8:40 AM To: [email protected] Subject: RE: hot air flues We are using 155° Res heads. The question is really the definition. We are in the process of changing them to 175° because of a inch and a half. 24" to the side of a hot air diffuser when both of us want to be in the middle of the room. This causes a problem but not like having a head go off because the heater came on. Thank you for your attention. Andy Johnston _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum