Todd, did you mean "TY-FRL", instead of "TY-FRB"?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jimmy Waite
Sent: Tuesday, December 19, 2006 7:44 AM
To: [email protected]
Subject: RE: both QR & SR sprinklers

Todd, 
It seems to me that maybe a better head for you to use would be a "SW-24" by
Tyco.  They are listed for coverage up to 16' x 24', and they are listed as
standard response.  Also, I don't believe that "TY-FRB" Sidewall can cover
16x22.

Jimmy Waite
Burtell Fire Protection, Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
Sent: Friday, December 15, 2006 4:02 PM
To: [email protected]
Subject: both QR & SR sprinklers

I have been looking at an existing hotel building where each guest room has
a Central GB-LO extended coverage sidewall sprinkler covering the sleeping
area and a Central Model H sidewall covering the space between the sleeping
are and the room door. Since the GB-LO's are under recall, they are going to
be replaced, most likely with Tyco TY-FRB K8.0 extended coverage sidewalls.
My question is this; the Model H is a standard response sprinkler and the
TY-FRB's are listed for both standard and quick response. Even though it is
listed for SR, I assume that the response time is in QR territory. Is there
going to be a problem mixing these two sprinklers? The demand area is the
two sprinklers and the FRB spacing is 16x22 and we are using UL criteria.

 

 

Todd G. Williams, PE

Fire Protection Design/Consulting

Stonington, Connecticut

860.535.2080

www.fpdc.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to