Good point Ro - I was thinking about the definition and speaking to Charles' question. If you're going to retrofit the building with sprinklers the standard allows you to substitute a 2.5" x 1.5" reducer at each Class I connection for the Class II hose stations. The 130' coverage requirement is specifically excepted as well.
Steve Leyton Protection Design & Consulting -----Original Message----- From: Roland Huggins [mailto:[EMAIL PROTECTED] Sent: Wednesday, December 27, 2006 9:17 AM To: [email protected] Subject: Re: Class III Standpipe SInce sprinklers are being added, what's the schedule for completion? If it's all part of the same job, why not talk to the AHJ and owner about just going with a Class I standpipe and do a manual-dry one? Roland On Dec 26, 2006, at 5:16 PM, Coastal wrote: > Hello sprinklerforum, > > I need to install a Class III standpipe in a location where it is > subject to freezing. I see a reference in NFPA 14 2003 section > 5.4.3 to a "Semiautomatic-Wet" but no definition for one. I am open to > suggestions. Looks like this little 4 story 32 room hotel is going to > be spending a bundle on the remodel work. > > I am unable to reuse the existing standpipe as it could require > passing a burning room the get to the existing location. The building > is not sprinklered now but they are being added throughout. > > -- > Best regards, > Charles Thurston > Coastal Fire Protection > mailto:[EMAIL PROTECTED] > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum