I didn't catch what size valve you have but 200 psi shouldn't be an issue since the deluge valves are rated for higher pressures. Model 758, 1-1/2, 2, 2-1/2, 3, 4, 6 in. sizes for vertical installation and actuator valve, Model 753 or Model S/776 for rated pressure of 300 psi. The Model 758, 8 in. for vertical installation and actuator valve, Model 753 or S/756, for rated pressure of 225 psi.
The Deluge valve, Model 758 1-1/2 through 6 in. for use with Model S004753006 electric solenoid valve for rated pressure of 300 psig. For operation by dry pilot, wet pilot, electric or manual activation. Hope this helps, Bob Robert Ballard Senior Project Engineer Victaulic Company of America 4901 Kesslersville Road Easton, PA 18044-0031 office: 610-923-3772 fax: 610-923-3065 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum