I didn't catch what size valve you have but 200 psi shouldn't be an issue 
since the deluge valves are rated for higher pressures. Model 758, 1-1/2, 
2, 2-1/2, 3, 4, 6 in. sizes for vertical installation and actuator valve, 
Model 753 or Model S/776 for rated pressure of 300 psi.  The  Model 758, 8 
in. for vertical installation and actuator valve, Model 753 or S/756, for 
rated pressure of 225 psi. 

The Deluge valve, Model 758 1-1/2 through 6 in. for use with Model 
S004753006 electric solenoid valve for rated pressure of 300 psig. For 
operation by dry pilot, wet pilot, electric or manual activation.

Hope this helps, 

Bob

Robert Ballard
Senior Project Engineer

Victaulic Company of America