Just a follow-up to the bfp point....

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, January 09, 2007 6:49 PM
To: [email protected]
Subject: Re: max velocity

Just as a side note Backflow preventors are tested and usually listed at
10 
Fps, if your exceeding the flow limits of the backflow preventor you can

damage it in full forward flow testing.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926

Thom-

An interesting point...But what are we to do with this information?  

I assume all of us take bfp pressure loss into account in our designs
using the mfg cut sheets and corresponding curves.  Presumably if the
mfg provides the curves, then that is within the acceptable range of
operation of the bfp and the design is fine.

Are you simply making the point that you can damage the bfp if you
perform some type of test that takes it out of its range?

Paul Sincaglia, P.E.
Firesafety Solutions, Inc.