Thank you for the information Art!

In Europe we say that centre of pump must be equal or lower than the lower
line for calculation net capacity in tanks. Therefore, we usually end up
with pump room floor lower than the bottom of the tank to minimize unusable
volume or we need to have to install pumps working with negative suction
head and install small tanks above the pumps to fill them with water if
necessary to avoid air in the systems (Negative suction is allowed but we
try to avoid it). 

Do NFPA have a similar rule concerning were the pump located and positive
head? (I could not find when I did a search in my PDF version) 

Some people over here argue that if one uses a vortex plate one can still
use this volume even if one have a pump room floor levelled with bottom of
the tank and as well be on the positive head. 

If I understand you correctly, they are wrong? 

Why am I telling you this, well now we (in Sweden) need to use NFPA rules
for EC sprinkler, ESFR, etcetera as well as our own standard (Swedish) which
are on top of European standard. It starts to be vary confusing with all
this rules and I just try to find some common ground.

I'm sorry for my bad English. I hope that you understand me.

Best regards/ Leif Glans

www.lg-sprinklerkonsulten.com

LG Sprinklerkonsulten
PG Vejdes vag 15
351 96 Vaxjo

Phone: +46 470-74 50 25
Fax: +46 470-74 50 26
Cell: +46 734-28 13 10


-----Ursprungligt meddelande-----
Från: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] För art
Skickat: den 15 januari 2007 20:23
Till: [email protected]
Ämne: RE: Positive static head for tanks

NO. As the tank empties or reduces to zero this head disappears. Assume the
tank is nearly empty. That is the static head. If the tank is on a hill the
elevation from base of the tank will provide you some static head.
Art
ATCO FIRE/Tiroly & Associates

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Leif Glans
Sent: Monday, January 15, 2007 12:26 PM
To: [email protected]
Subject: Positive static head for tanks

Hi!

If one uses Centrifugal Pump according to NFPA 20, one should not use it if
static suction lift is required (6.1.2, A 6.1.2)

According to NFPA 22 4.1.3 for suctions tanks, the net capacity shall be the
number of cubic meters (U.S. gallons) between the inlet of the overflow and
the inlet of the vortex plate 

Is all of this volume considered positive head according to NFPA?



Best regards/ Leif Glans

www.lg-sprinklerkonsulten.com

LG Sprinklerkonsulten
PG Vejdes vag 15
351 96 Vaxjo

Sweden

Phone: +46 470-74 50 25
Fax: +46 470-74 50 26
Cell: +46 734-28 13 10




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to