Thanks Tom,
We do have a water only system.  I will go through the chart and confirm what I 
need.
How would you determine the "expected discharge" from the sprinkler system. 
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom L
Sent: Monday, January 15, 2007 6:40 PM
To: [email protected]
Subject: RE: NFPA 30 (03ed) - curbs

Dewayne,


So do you have a foam system or not? If you do then curbs without drainage is 
OK If you have a water only system then u will need drainage with the curbs.

Review figure 6.8.5 on page 57 of NFPA 30, 2003 edition, it will indicate IF 
you need to provide spill containment OR liquid spread control. Curbs are used 
if you have a closed head foam system to control the spread of the product 
mixed with the water (section 6.4.2.5). If you have a water only sprinkler 
system and you have a Class I-IIIA liquid then, you need to provide liquid 
spread control as per 6.8.5.1.


Take a look at FM data sheet 7-29 it has more up to date sprinkler protection 
requirements then NFPA 30/ 2003 edition.

Regards

Tom

Chubb Insurance

>From: "Dewayne Martinez" <[EMAIL PROTECTED]>
>Reply-To: [email protected]
>To: "SprinklerFORUM" <[email protected]>
>Subject: NFPA 30 (03ed) - curbs
>Date: Mon, 15 Jan 2007 10:51:03 -0600
>
>Section 6.4.2.5 deals with curbs, scuppers, special drains, ect....and 
>states that "If a drainage system is used, it shall have sufficient 
>capacity to carry the expected discharge of water from the fire 
>protection systems and hose streams."
>If there is only curbs does this apply since there is technically no 
>drains?  If so, what is the proper way to determine the expected 
>discharge?
>Thanks,
>Dewayne
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Type your favorite song.  Get a customized station.  Try MSN Radio powered by 
Pandora. http://radio.msn.com/?icid=T002MSN03A07001

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to