NFPA 13, 2002 (12.1.1) and 2007 (12.1.1) state that "Sprinkler
protection criteria are based on the assumption that roof vents and
draft curtains are not being used."  Obviously, if roof vents aren't
being used, then fans that may be on at the time of a fire would not be
considered in the design criteria either.  Since the 13 criteria isn't
based on fans operating then I'd recommend against them. Manually
operated fans for F.D. operations only, maybe.

Scott Futrell

(763) 425-1001 Office
(612) 759-5556 Cell