Ed,
Here in Vegas we do things that may not be done elsewhere.  The
International Building Code requires a minimum headroom be maintained
throughout the stair and landing.  The minimum headroom is 80 inches.
If you keep the control valve above this height (allowing that you have
the space needed) keeps you out of trouble with clear widths and
projections into the exit path.  If you don't have the space needed, we
have been moving forward with the floor control valve in the vestibule
and the hose connection in the stairwell.  The vestibule is required to
have 44 inches of clear width so we have been recommending the clear
width be provided between the supply piping and opposite wall.  This way
you meet both the headroom and clear width requirements for exiting.  

 
Carl Chappell
Associate
101 Convention Center Dr. Ste. 650
Las Vegas, NV 89109
Phone: (702) 699-5391
Fax: (702) 699-5534
Cell: (702) 400-8736
www.rjagroup.com
 
(This electronic message contains information which may be confidential
or privileged. If you are not the intended recipient of this message, be
aware that any disclosure, copying, distribution of use of the contents
of this information is prohibited. If you have received this electronic
transmission in error, please immediately notify the sender at the above
phone number.)

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, January 25, 2007 9:38 AM
To: [email protected]
Subject: Floor control valve heights

Prestigious forum members: 

NFPA 13 and 14 don't give guidance on the height of sprinkler floor
control
valves located exposed-to-view inside stair towers.

Any recommendations from owners or AHJs?  

Any horror stories due to them being too high or too low?

Ed Kramer
Littleton, CO


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to