24.4 (2)

Tony Liddic
AEC Fire & Security
400 Fame Rd.
West Carrollton, OH  45449
937-866-4158
937-865-0212 fax
[EMAIL PROTECTED]


-----Original Message-----
From: Brian Harris [mailto:[EMAIL PROTECTED] 
Sent: Monday, January 29, 2007 2:43 PM
To: [email protected]
Subject: RE: Drum drip (condensate trap) maintenance in dry system

Ed,
Any idea where that is in NFPA-13 2007 ? It's always been there in 03 but I
don't see it in 07.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Monday, January 29, 2007 2:28 PM
To: [email protected]
Subject: RE: Drum drip (condensate trap) maintenance in dry system

To expand a bit on Matt's comment - the contractor is REQUIRED to provide
you with a copy of NFPA 25.  If he BS's you, ask him to break out his NFPA
13 (the design standard for your sprinkler system) and the two of you can
review section 16.4(2) together.

Ed Kramer
Littleton, CO

>
>If you are the owner , the contractor should have provided you with a copy
>of NFPA #25. If they are an astute contractor, they would have asked you
>to
>sign a piece of paper stating that you had, in fact, received a copy of
>25.
>In any event. www.nfpa.org has copies for sale, not very much. Or you
>could
>always ask for your copy from the contractor. In this manual you will find
>ALL of the items required for the owner of a sprinkler systems.
>
>R/
>
>Matt


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


-- 
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.432 / Virus Database: 268.17.12/655 - Release Date: 1/28/2007
1:12 PM
 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.432 / Virus Database: 268.17.12/655 - Release Date: 1/28/2007
1:12 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to