Yeah, I don't know why we couldn't use the valve from the floor below. For horiz. SP we could you two valves as well. Why design for 250 gpm at the most demanding valve if it's to be tested at 500 gpm?
Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Wednesday, February 07, 2007 7:21 AM To: [email protected] Subject: RE: NFPA 14 - 2003 Great question. I have seen them both ways but the local AHJ's allow us to use the one at the top and the next one down to facilitate testing. Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, February 07, 2007 8:17 AM To: [email protected] Subject: NFPA 14 - 2003 It has been a while since I have delved into 14 and I can't get into AFSA's archives so please bear with me. 7.3.2.2 An additional 65-mm (2 -in.) hose connection shall be provided at the hydraulically most remote portion of the system to facilitate testing. Does this mean we have to have two 2.5" hose valves at the top of a standpipe? What about horizontal systems? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum