Todd,
Is your water supply good enough that you don't really need the pump for
sprinklers on the lower level or two?
Jeff Hewitt, PE, SET, SFPE (Prof. Member)
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any use,
disclosure, copying or distribution of this e-mail is unauthorized. If you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Todd Williams - work" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 07, 2007 11:10 AM
Subject: RE: pump tricks
That's fine for the flow, but when you add the static pressure of the
water supply with the churn pressure of the pump, you can get real close
to the 175 psi threshold. This is problem increases as steepness of the
public water supply curve increases.
At 12:01 PM 2/7/2007, you wrote:
This does not compute.
If you have a six-story building it's what, 70' high? With static and
friction head, that shouldn't be more than about 40-43 PSI from the
street, unless you're using 3" risers ...
And remember that the 100 PSI is at the discharge side of the valve; most
hose valves have at least 3 PSI and sometimes as much as 7 or 8 PSI head
loss (we've had this discussion on-forum before).
Steve
-----Original Message-----
From: Todd Williams - work [mailto:[EMAIL PROTECTED]
Sent: Wednesday, February 07, 2007 6:22 AM
To: [email protected]
Subject: pump tricks
I seem to be running into several situations lately where there is a
very fine balancing act between meeting the 100 psi at the top outlet
of the standpipe and not exceeding 175 psi at the base of the riser.
(6 story hotels are a good example) Does anybody have any good ideas
they'd care to share on making these work? I'd like to limit the use
of extra-heavy pipe and fitting (especially larger sizes) and PRVs. I
have several tricks up my sleeve, but I'm running out of sleeves.
Todd
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum