Carol:

Heavy timber is still "combustible construction" so your design area will increase, and by your description you'll have a ceiling full of 56" deep pockets, which would each require a sprinkler head, since you'll be unable to meet separation (10lf Horizontal) or maximum depth (36") and is not of un or limited combustible construction as stated in exemptions for ceiling pockets in 8.6.7.2. Also see 8.5.5.2 and 3.7.1 & A3.7.1 (2002)

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Carole Holmes" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, February 08, 2007 4:18 AM
Subject: RE: pockets vs obstructed


I am currently looking at the same situation, only rather than a restaurant
I'm at an OLD grain mill.  It's now being renovated but trying to keep as
much as they can from the Mill.
My "lego" ceiling will be located in a flower shop and the pockets are 5'3 x
4' and are 56" deep!  My heart stopped when I looked at it.  Here's the
kicker, it's all heavy timber.  So, are sprinklers required?

Carole Holmes
Kalamazoo, MI

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, February 07, 2007 10:44 PM
To: [email protected]
Subject: RE: pockets vs obstructed

Greg - What's the spacing of the sides of the 'lego's'?  If they're 3' to
7.5' on-center, it likely does qualify as obstructed construction.  And if
they're not more than 22" deep (or close to that), sprinkler spacing should
be fairly simple.

Ed Kramer
Littleton, CO


The ceiling looks like the bottom of my sons lego's!
How many soffits / pockets does it take to consider a ceiling obstructed
construction rather than trying to protect every small pocket?


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to