IBC Section 3311 (Safeguards during Construction) provides the requirement. 3311.3 directs us back to IBC Chapter 9. IBC 905.3.2 provides the 200 ft "reach" requirement in buildings exceeding 10,000 s.f. in area per story.
John Drucker Fire Protection Subcode Official New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, February 08, 2007 4:37 PM To: [email protected] Subject: Temporary Standpipe Forum (Steve or Rich), Must all portions of a floor be within 200 ft. reach of a temporary standpipe valve? Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum