That's what I was thinking. Required is 12" below frost line and Figure A
10.4.1 is recommended.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of art
Sent: Friday, February 16, 2007 7:19 AM
To: [email protected]
Subject: RE: Depth of Cover

Use the NFPA required depth of cover.

Art

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Randy Knutson
Sent: Thursday, February 15, 2007 2:21 PM
To: [email protected]
Subject: Depth of Cover

If I know what my frost depth is locally do I have follow Figure A 10.4.1 in
NFPA 13?

Our local frost depth is 24". Per NFPA 13:10.4.2 "The top of pipe shall be
buried not less than 1 ft. below the frost line for locality."

That gives me a 36" depth of bury from top of pipe.

 

The local AHJ saying that it has to have 4'-6" of cover because that is what
is shown in figure A 10.4.1. 

 

I'm arguing that this is a recommendation to be used if you don't have your
frost depth for your locality.

 

He says the Figure A 10.4.1 gives the required depth.

 

Please help. 

 

Thank you,

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum