Terry,

In full scale fire testing involving 4 ft. wide solid shelf racks 12 ft. high protected by Large Drop sprinklers at 25 psi, the fire spread the full length of the ignition rack, jumped the aisles, and spread the full length of the adjacent racks.

Sprinklers located beneath grated mezannines over aisle spaces between shelf storage racks are essentially useless. By the time they operate, the fire has spread beyond them both horizontally and vertically. This is precisely what happened in two record storage fires a few years back.

Joe

Terry King wrote:

I have miscellaneous storage of auto parts in a car dealership.  It is
mostly shelf storage (less than 30" wide) but there are a few racks with
solid shelves.  The maximum storage height is 8'-0".  Do the
requirements for sprinkling beneath the solid shelves apply to racks
that are only 8'-0"
high?  Can someone show me where I might find this in 13? (I have
conflicting opinions around here).

All of this storage takes place under a grated mezzanine which has
sprinklers between each rack and/or shelf.