Pardon my digression...
One of things I know puts me out of price, bid-wise is FDC locations.
I feel they should be locate on the street address and run independently to
the controls.
They should have signage over and above what the escutcheon says.  I have my
own.
I have the word "liability" tattooed to the underside of my eyelids.
I won't bid and install something I feel is wrong or a possible liability
issue.  I'd rather stay home.
I wish NFPA 14 said "it shall be this way" on multiple systems, and others
as well.
Maybe it's another time for a committee proposal.

Tom Duross
Go Red Sox!

-

I realize that the added expense of running hundreds of feet of additional
pipe to interconnect the risers may seem exorbitant. But Stop and think a
moment. Every day we run thousands of feet of pipe to ensure these
properties are protected, but we're not willing to run a couple of hundred
feet of additional pipe to ensure that these systems will perform, with
minimal training the way they are expected to by both the owner and the FD?
Maybe this needs to be submitted to 13, as Ed said, but doing what is right
has never been limited by "The standard doesn't say I have to!" (I just
can't get that Winnie text to sound as good as Steve L. can) Sitting down
with the owner and the AHJ and reviewing the situation, and reasons to do it
right, may have your owner opening his wallet, to save the AHJ from getting
something he doesn't want and won't work for his FD.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926

That is why if there are multiple risers it just works out best to
provide a single FDC at the backflow or at some designated point on the
UG system if it's a private loop, but if the building is large enough to
warrant multiple risers but is fed from a municipal system, then a
common FDC or FDC tied together is not practical.   Signage at risers
and a good walkthrough of the facility with the local FD is about the
best that can be done.  Running hundreds of feet of pipe inside the
building between risers to connect FDC's is just a bit over the top.

>From an AHJ point of view more than one FDC on a Building that only
>supplies
a portion of that building is always a bad idea. Late at night, maybe
snowing they drive up to the building, see an FDC, but the strobe or
water motor above it isn't flashing or making a sound. They have the
right address, even if no smoke or flame is visible, they will still
hook up to it before entering the building, guessing that the strobe is
broken or water motor broken. Now we've put them at risk, because they
don't have time to drive all the way around the building to see if there
is another strobe flashing somewhere, or another FDC.

This is just a bad idea!

> Run into something new that I need opinions on.
>
> An addition is being added to an existing building.  Existing building
is
> fully sprinklered.  The total area of the combined existing and new
> structure exceeds 52,000 sf and the existing system riser is in the
far
> corner away from the addition.  So the decision was made to bring in a
new
> underground supply to serve the new addition.  Thus the new addition
will
> have its own independent system riser and fire department connection.
>
> Does 2002 NFPA 13 section 8.16.l2.4.3 (or any other section) require
the
> two FDCs (one existing, one new) be tied together?
>
> The commentary hints at this, but I've never thought that was the
intent.
> I thought the intent was that multiple systems SERVED BY THE SAME
> UNDERGROUND LEAD-IN be served by the same FDC.  Section 8.16.2.4.5
seams
> to
> support this.
>
> Opinions?
>