It may be a separate "structure", but is it a separate "building" in accordance with the applicable building code? If it is like most hotels with a couple of feet between these structures, it is very unlikely to be a separate building.
Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rod DiBona Sent: Friday, March 02, 2007 12:50 PM To: [email protected] Subject: RE: Porte cocheres Well I agree with you Joe. I am certainly not an expert on the building code but I sure find myself in the IBC consistently. At this point I still have to say that I believe that this combustible porte cochere ( car port ) is a separate structure that does not require sprinks...same as you. The fire marshall has not responded back to me as to why he believes it needs to be covered but I am trying to do my homework in the meantime. I have simply asked him to show me in the building code where and if it addresses this. Thanks for the input. Any other thoughts? -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Friday, March 02, 2007 9:42 AM To: [email protected] Subject: RE: Porte cocheres I think the answer is found in the building code, not NFPA 13. When I started the trade I knew nothing about the building code let alone owned one. Now I don't know how you can even design without one and I wonder if a few architect and engineers even look at it. The porte cochere is most likely a utility or Group U occupancy. From the 03' IBC "312.1 General. Buildings and structures of an accessory character and miscellaneous structures not classified in any specific occupancy shall be constructed, equipped and maintained to conform to the requirements of this code commensurate with the fire and life hazard incidental to their occupancy. Group U shall include, but not be limited to, the following: Agricultural buildings Aircraft hangars, accessory to a one- or two-family residence (see Section 412.3) Barns Car ports Fences more than 6 feet (1829 mm) high Grain silos, accessory to a residential occupancy Green houses Live stock shelters Private garages Retaining walls Sheds Stables Tanks Towers" Your situation I would think would be a car port. That being said I see it as a separate building or structure and sprinkler protection is not required whether it's combustible or not unless there is something in the IBC about proximity and exposure to the main structure. I think it's best left up to the Building code official. If it can be shown in the code where sprinklers are required for the accessory structure. Just my opinion. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rod DiBona Sent: Friday, March 02, 2007 9:06 AM To: [email protected] Subject: RE: Porte cocheres That is what I am trying to find Craig. At what point do we still have to sprinkler a detached porte cochere. I can't find a definition in NFPA or the IBC that describes a porte cochere to see if it is by definition attached. What if it is 30' from the motel do we still have to sprinkler it? I don't think so....I studied NFPA 8.15.7.1 thru 8.15.7.5 but now I am thinking that those references are talking about when the "porte cochere" is attached. Obviously an exterior roof and the canopy are attached so why would this standard in the same section apply to another structure that is not. If it is a separation issue I would like to know where the line is drawn...3ft, 10ft, 40ft?? Hmmm. I will be looking at the IBC. Any thoughts? Thanks. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday, March 02, 2007 6:32 AM To: [email protected] Subject: RE: Porte cocheres Ruling we had was that combustible then sprinkle. If not combustible we did not have to sprinkle as long as the cars were there only temporarily for pickup or drop off, not long term parking. If yours is detached and combustible he could be citing separation issues as listed in the IBC that can dictate the need for sprinklers in the PC. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rod DiBona Sent: Thursday, March 01, 2007 6:20 PM To: [email protected] Subject: Porte cocheres Is there any clear cut building code or nfpa standard that addresses sprinklering porte cocheres?(normally the drive under entrance for motels) I had the understanding that if they are attached and combustible they needed to be covered but if they weren't BOTH that they didn't. I have an "unattached" combustible porte cochere at a motel where the fire marshal has asked us to sprinkler it from the dry system in the attic. Thank you for your input. Rod DiBona Rapid Fire Protection _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum