Greg,

I have calc'd numerous test headers at distances from 16ft to more than
100' from the fire pump discharge.
I have never had an instance where the calc's did not work with.

I am sure there must be a situation that has concerned the NFPA
committees enough to include the requirement, but I do not know what it
is.

Thanks,

Ray Vance 
Chief Engineering Tech
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, March 02, 2007 2:54 PM
To: [email protected]
Subject: fire pump test header size



Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
This is from the 2007 edition of NFPA #20.

5.19.3.4 Pipe Size. The pipe size shall be in accordance with one of the
following two methods: 

(1)      Where the pipe between the hose valve header and connection to
the
pump discharge pipe is over 15 ft (4.5 m) in length, the next larger
pipe size than required by 5.19.3.1.3 shall be used. 

(2)*      This pipe is permitted to be sized by hydraulic calculations
based
on a total flow of 150 percent of rated pump capacity, including the
following:                                                         

(a)      This calculation shall include friction loss for the total
length
of pipe plus equivalent lengths of fittings, control valve, and hose
valves, plus elevation loss, from the pump discharge flange to the hose
valve outlets. 

(b)      The installation shall be proven by a test flowing the maximum
water available. 


I just calculated a test header located approx. 65' from a 750 gpm pump
and it seems to work easily with 6" pipe flowing 1,125 gpm in lieu of
increasing the pipe to 8". Has anyone got experience using this method?

Space is the issue and 6" works much better then 8" in this situation.


Thanks,
Greg McGahan

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to