To do a follow up with the forum... I did as you suggested Thom and I did a calc in the remote area, 900 sq. ft. and then another covering the waiting/lobby area and 7 heads in the corridor. The savings will be great at least for the size of the project. 2-1/2" mains and 3" riser with a single snoot instead of 3" main with 4" bulk to the 2nd floor and a 4" riser. Thanks to everyone for all your help, Kathryn
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, March 05, 2007 9:33 AM To: [email protected] Subject: Re: Reduced Calc Areas I think that this is a unique situation which I would discuss with the AHJ. In the past with a similar small lobby and open hall, we have calculated the heads in the lobby and up to 7 heads in the hall. NFPA 13 2002 11.2.3.3.8 Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Kathryn Tyler" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, March 05, 2007 8:06 AM Subject: RE: Reduced Calc Areas >I do realize that, but what if the areas in the remote areas contain heads > in the corridor which is open at one point to the waiting room which has a > ceiling exceeding 20' ion height? Would I then calc the existing areas > utilizing the % reduction and then calc the high ceiling and surrounding > areas at 1500 sq ft? Even when there are only 2 heads covering the area > with the high ceiling? > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Scott > Mitchell > Sent: Friday, March 02, 2007 5:29 PM > To: [email protected] > Subject: RE: Reduced Calc Areas > > Chris: No - but it would be the AHJ's prerogative to require a separate > hydraulic calculation for the mechanical room. > > Kathryn: Your hydraulic calculation using a QR design area reduction is > only valid for those portions of the building with ceiling heights used to > set the % reduction. If an area's ceiling height exceeds that, you have to > do a separate calculation for that area. > > Regards, > Scott Mitchell > > Chris Brown <[EMAIL PROTECTED]> wrote: > Would you space all the sprinklers 130 sq. ft. throughout because of a > mechanical room with the building. > > > Thank you, > > Chris Brown > Fire Protection Designer, Poole Fire Protection > Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax: > 913.829.8690 > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Kathy Tyler > Sent: Friday, March 02, 2007 9:31 AM > To: [email protected] > Subject: Reduced Calc Areas > > Our firm has a job where two of the designers (co-working on the > project) in my office made a decision to not reduce the hydraulic calc > area > per using Quick Response heads because of a small waiting area that is > open > to both floors, (this building has only 2 stories) which would make the > ceiling height exceed 20' as allowed. However I am reviewing the design > prior to going out and I am questioning their decision and would > appreciate > the Forums feedback. > There is an area at the entry of the bldg and it is 162 sq. ft. and is not > included in any of the two remote areas on the 2nd floor being calculated. > However the remote areas do include heads in the corridor which is open to > the waiting area which has the high ceiling. > Do you feel that because of this high area that all calculations should > not > be allowed to be reduced or should be? > Thank you in advance, > Kathryn > > Kathryn A. Tyler NICET IV, ASCET Member > fire protection designer > Kelly-Wright & Associates PC > Hvac, Plumbing & Fire Protection > (520) 887-1919 ext. 302 > fax: (520) 696-0280 > [EMAIL PROTECTED] > www.kwmech.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > --------------------------------- > Bored stiff? Loosen up... > Download and play hundreds of games for free on Yahoo! Games. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum